T

thepurple1

I am refurbing an old BMS control panel the panel is about 15 years old and had Satchwell controls in, I am now fitting Trend I have been told that the controls/ panel never really worked. I have got half way through the refurb and I have a problem with the 0-10 volt signals, they seem to do what they want but not all the time. The cable is the existing cable and os screened where necessary. The 24 volts on the secondary side of the transformer has the o volts grounded as normal. I have 240 volts to earth -ok and 24 volts to earth-ok. on the Neutral to earth I have 0.3 volts to earth, on the secondary side of the transformer I have 0.3 volts to earth could this be a problem?
The panel is in a hospital with a mobile C.T scanner parked out side in a lorry it looks as if the power for this comes from the hospital. Could this be the problem, can a C.T scanner cause interference with certain a
electrical items?
Any kind of help or pointers would be good as I am lost
 
Is the trend unit properly programmed ?

Are you on about inputs or outputs from the trend (0-10Vdc)

Whats the sensor (0-10V) make and model ?
 
Yes the Trend is programmed and I'm in the process of commissioning it, it is not a programming issue. The problems are the outputs to the 2RM's and the inputs from the 4DIX's. The 0-10volts to the valve actuators seem to be ok
 

Reply to Control panel problems in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

I want to connect one panel 12 volts (south west) with 2 panel that are in series 24 volts (south) in parallel to a 24 volts in controller. The...
Replies
0
Views
649
Just doing some thread admin :)
Replies
1
Views
802
  • Question
i saw a good description recently where it said that BS7671 is directly referenced in other legislation which I haven’t seen before and it better...
Replies
20
Views
3K
  • Question
I've done the board change on this now, what a lash up it was before, old 16th board hacked into a dual RCD one, think they have taken the main...
Replies
7
Views
1K
It is highly unlikely you are getting the sensation of electricity. The pan is isolated from the induction coil by the glass top, any voltage...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks