I've been in the industrial maintenance 'game' since mid '94 so seen a fair few panels, main control panels that is. As some here may recall, I'm larking around trying to outdo C&G in creating a structured electrical apprenticeship program for our recruit, so am looking back over my time.

I'm still learning so this is an opportunity for me to reinforce my understanding of things and also to remember most of what I've forgotten!

Ventilation! What's the general view on forced-air ventilation? Fan to blow in or suck out?

Drives (VFDs). Low for cool air or high up where heat rises before expelling out through vent?

PLCs. Low down in cooler air or at top (seems to be quite common with a viewing window!)?

.
 
Manuf' instructions 1st mate!

Which ever air removal method you use you need to allow for make up air.

IMHO the air in or air out depends on your environment.

VFD's/Inverters.Servo drives, again manuf' instr, but, do you want the hot air of the heat sinks affecting the rest of the panel ir high up being sucked straight out?

PLC's bit more difficult, out of any humid air stream caused by panel air con.

This is more of a thermal engineering Q than an electrical, and I don't think this is taught on ANY electrical course TBH!!!
 
I prefer filtered air forced in. Any leaks around doors or panel sections have air forced out and not drawing dust in. I’ve always worked in dusty environments so it’s been a constant battle. We had a new engineering manager and he couldn’t understand why I’d banned the use of switch grease on one plant, he found out at the next shutdown when a combination of grease, heat and cement dust had glued main switches closed.

VFD’s near the top so there’s room for associated control gear in the relative cool at the bottom.

PLC’s at eye level. OK maybe not my eye level.
 
was called to a brand new machine tonight and it took longer to find the electrical enclosure than it did to rectify the problem, but this enclosure was the opposite of what Tony prefers, air out, VFD's at the bottom and PLC above eye level, (i'm a short ---), guess it depends on the enviroment, have worked around industrial ovens where you certainly wouldn't want to blow air in because of temperature but also because baking flour hung in the air.
 
Hot environments are a nightmare. I’ve worked on over 40 kilns and furnaces, all panels would be remote to protect them. But sometimes a local panel couldn’t be avoided but if possible air would be ducted to them or low-pressure compressed air blown in. Dust has always been the bane of my life!

BTW how’s the new job going?
 
BTW how’s the new job going?

Thanks for asking... I chose to remain with the Black Stuff... long story cut too short but this apprentice thing was a huge factor in me staying put! Also 'better the devil...' in the current climate!

Back to these control panels...

We have a KHS filler. The panel fan is blowing air in at the base of the right hand door. There is a filter in the grille. The air is then expelled at the top of the left hand door. Immediately in front of the fan (obviously when door closed) is the main drive motor protection and supply isolation transformer. After recent floor work the fan had drawn in a concrete mist so everything was covered in crud.

Another thing in the bevvy-boxing industry is the ability for the panel ventilation to draw in a tar-like air and coat the gubbins. Everything becomes sticky!

One of the things I'll be doing with the App. initially is to go around parts of the plant and open up a number of panels. So that he becomes familiar with layouts and components we'll note locations of devices and collate some evidence that we'll look over at the end of the task. We'll test some voltages within the panel and basically get him quickly accustomed to potential dangers and have him become "respectfully confident" around live equipment (safety being paramount and extreme supervision being a novice!).

Thanks so far guys.
 
Last edited by a moderator:
New to the forum, my background is in industrial electronics,

I have attached a good guide by hoffman on the subject

the main issue is that if the cabinet overheats the life span of the electronics can end up being severely degraded, usually they just get through the warranty period and fail !

we use the battery powered usb loggers by lascar which log the temperature at settable sampling rates. these things are worth their weight in gold for spotting problems.

there are many panel manufacturers who have fan sizing software to calculate airflow on their web sites.

as an exercise for your apprentice, get one of the loggers from rs or farnell and get him to do preventative maintenance on all the electrical cabinets, it will save you an absolute fortune !


regards
lman_271860
 

Attachments

  • Spec-00488.pdf
    551.5 KB · Views: 51
Welcome to the forum and thanks for the info... good suggestion is that. We do (are supposed to) panel temp & humidity checks... yawn... yeah I know.

.
 
I replaced a load of obsolete interface relays in said Filler panel approx. 18 months ago. You know the Siemens slim-line ones. A nice battleship grey colour with the signature bluey-green logo and label strip. They have since turned a shade of beige.

A colleague replaced some other type of relays the other night. He said they just crumbled when he attempted to undo the terminals!
 
I have been working on the same reliability and maintainability project across quite a few automotive and aerospace companies and have seen some infant failures on very expensive machine tool spindle and servo systems.

when the manufacturers specify a maximum ambient temperature for drives most people assume that would be related to the average cabinet temperature but .............................
you really need to read the small print !

you will find a maximum air inlet temperature at the bottom of the heat sink at the drive !!!!

when we monitored the inlet temperatures they exceeded manufacturers specification therefore NO WARRANTY CHACHING :p

in this case the cabinet was completely sealed and being chilled with rittal air conditioning units set to 35 Celsius and was happily reporting everything was aok.

the solution to the problem was simple we made some ducting to route the chiller air straight under the drives

regards
lman_271860
 
lman,
You may well have worked with my previous employers kit then, two of them in fact.
One was an automotive machine tool builder, the other was a manufacturer of CNC/PLC/Servo & inverter systems.
Yes we did specify a maximum inlet temperature for the heat sink.
Oh, we could tell too, or at least our workshop guys could.
A lot to do with electrolytics drying out at elevated temperatures.
 
NetBlindPaul,

electrolytic capacitor degradation is a very interesting subject and is usually the root cause of a very high % of all electronics failure

the temperature rating on high frequency low ESR caps is only valid for 2000 hours only IE about 3 months !

lman _271860
 
Paul for gods sake never go in to steel making. High temperature shut down? I’d have been hung from the nearest beam for even suggesting it. A warning maybe, that can be ignored, but a shut down, no chance!

A one inch air line blowing in to the panel usually cured the problem. If thing went badly wrong it was a case of do anything you could to get it going again.

One catastrophic failure cost £5M to get us back on line.
 
Tony,
These panels went into manufacturing plants into continuous process lines.
The client agreement was received, in fact it was endorsed, and it became their de-facto standard.
The panels, did have door mounted air con units mind, with filtration obviously.
I have worked in steel, don't like it but have done it and may be doing some more shortly.
The systems were designed to shut down in a controlled manner, and thus would bring the whole line to a controlled stop automatically.
It was not my design or concept, it was done elsewhere in the company, however, it was the company standard, and they are still going today and still manufacturing in the UK.
I understand your concern Tony, but, it depends on the value of the kit that you are protecting vs the cost of a line stop.
There were buffer areas in the line so one section shutting down would not stop the whole line instantly.

When you look at an unplanned catastrophic failure against a controlled shut down with prior warnings, remembering that there would be a time window between the warning and the over temp shut down so that action could be taken then the latter could easily be preferable depending on the industry and line design.
 
The controls panels on the machinery I work with dont have any temp monitoring equipment in or high temp shutdown.

The VFD's are mounted low (lenze, or telemeq units), with the plc (S5 or S7 generally) mounted high. No fan or forced cooling although there are a couple of 20mm vents on either side of the panel - some do have a panel heater in though.
 
Paul,I'm wondering whether you were involved with building the panels for the frontors we used in Swansea plant (mainly disc cutting).

They all had panel temp monitors thermostatically controlled.in the summer with no aircon in the building the 840c HMI continually had the fault "panel temp alarm" up on the screen.
After creeping the thermostat up all shift on hot days finally the aircon man got called in and it was sorted,well,for a little while.
Eventually the fault got downgraded in the HMI to a "message" rather than an "alarm".
40 frontor univerter machines all with flashing red lights but still going throughout the hot months after that!!!

In ford Swansea plant maintenance was a very dirty word!!!
 
In ford Swansea plant maintenance was a very dirty word!!!

Things have changed a great deal then, As my experience is quite different to say the least!! Big annual budgets and new plant was the norm. As you would expect, ... when down times costs thousands per minute. Which will probably be even more these days!!!
 
Things have changed a great deal then, As my experience is quite different to say the least!! Big annual budgets and new plant was the norm. As you would expect, ... when down times costs thousands per minute. Which will probably be even more these days!!!

I'm pretty certain we were relatively unique in that respect,especially visiting all the other ford plants and seeing how they do it.
The importance of non production loss was also big in their minds,but it was more a sticky plaster fix than anything else.
Generally budgets appeared limitless,I never remember having to struggle for spares that must have been worth millions,but their motto was "if it ain't broke don't fix it",not always a bad thing I suppose!!!!
 
The ONLY time sticky plaster fixes were condoned, was to get production back up and running. Directly that production shift had ended, maintenance teams would be correcting/replacing whatever the problem was that caused the down time on production.

Rarely was a sticky plaster fix still in place, by the time the following production shift began... Any major works that arose from down times would have been completly remedied over the weekend down time on over time...
 
E54,
Trust Vaughant & myself when we tell you Swansea was a different ball game.
It was run to failure sticking plaster, then run to failure.
They ran 3x5 shifts with O/T to make quota.
Rarely was there any such repairs as you describe, even when I was there as a vendor engineer telling them that these things had to be done.
It was always the quick fix, edit the plc to put a force in etc. never find the faulty switch or cable etc. and change it unless you had to.
Maybe this was one of the reasons the plant was devolved off to Visteon, and is now no more!


BTW,
I have also worked in BEP, DEP, Halewood, Jaguar Browns Lane, Land Rover E&N, Longbridge, Cofton Hackett, and several others, and I must say Swansea had pretty much the worst maintenance attitude when it came to root cause fixes.
 
Last edited:
Quite amazing how different plant locations can have such different philosophies on maintenance attitudes!! I can honestly say, hand on heart so to speak, say i just don't recognise the philosophy you have described at Swansea in my own personal experience of the company...

They were plowing millions in to new plant and automation of the paint shop right up until the final year of production at Dagenham. I know that, because i was involved in the installation planning of one such system in the final years. Thee project was called ''LEADLAP'' computerised vehicle scheduling system, it was around 96/97 as i remember. Long story that one...lol!!! Still have a letter of personal reference they forwarded to me with my completion bonus payment check ...lol!!

Now while i was back there, things had changed, re-organisation of the maintenance departments into a central location etc. But maintenance still very much at the forefront, as the system that was being installed, was designed around aspects of ease of maintenance and production fault location requirements...

That was a 4 month project, ending in the 3 week annual shutdown where everything came together and being fully operational on day one of the first day shift following the shutdown. Most of the containment, cabling, and panels etc, were being installed during the the weeks and months prior to the shutdown. Installation work being mainly carried out by contractors with the maintenance being given training on site and at suppliers establishment.

I'm ranting on now...lol! But the difference between my experiences and yours is like the proverbial ''Chalk & Cheese'' :cheesy: ...haha!!!
 
They did away with maint at Swansea quite a few years before they closed, around 1988/89 IIRC!
From then on all guys were in line teams, fitters, sparks, operators all doing maintenance and operating, cleaning etc.
 

Reply to Control panels in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

B
Ford Transit T280S Van For Sale ONLY £3990 NO VAT New Shape 57 Reg Dec 31 2007 Short Wheel Base Medium high roof 75000 genuine miles MOT end...
Replies
0
Views
2K
BlueToBits
B

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks