please stay with me, still learning !! Going to a family member to replace cooker and hob.
Current set up,
C/U to Cooker switch 6mm.
Cooker switch to outle plate to Hob 6mm
Cooker Plugged into 13amp ring
40a MCB
The new cooker, is 2.3kW
Hob is 5.8kW
Total Power : 8.1kW - 36amps
With Diversity : 17.8amps 22.8 if with plug socket
I am looking at connecting both hob and cooker to the cooker outlet plate from the cooker switch as with diversity, the 6mm cable is more than capable and is allowed as per 8.4 of the OSG but question is from Cooker outlet plate should I be using 6mm for both the hob and oven to the cooker connection plate as they will joined or should can i reduce the size of cable to flex/1.5mm for the oven as its only 2.3kW? Thinking its going to be tight with 3 x 6mm cables!
Many thanks
Current set up,
C/U to Cooker switch 6mm.
Cooker switch to outle plate to Hob 6mm
Cooker Plugged into 13amp ring
40a MCB
The new cooker, is 2.3kW
Hob is 5.8kW
Total Power : 8.1kW - 36amps
With Diversity : 17.8amps 22.8 if with plug socket
I am looking at connecting both hob and cooker to the cooker outlet plate from the cooker switch as with diversity, the 6mm cable is more than capable and is allowed as per 8.4 of the OSG but question is from Cooker outlet plate should I be using 6mm for both the hob and oven to the cooker connection plate as they will joined or should can i reduce the size of cable to flex/1.5mm for the oven as its only 2.3kW? Thinking its going to be tight with 3 x 6mm cables!