C

Chrisarm5

Hi All

I've recently been doing a kitchen re-wire, everything done, sockets added to ring etc. however for the cooker ive wired a 6mm radial to a cooker switch, then 6mm down to a single socket. As cooker is 2.7kw this is acceptable on a 13a plug top....is this correct?
However now the customer has decided to tell me they're getting a separate electric hob, (this is after 2nd fix) and walls plastered. The info I have on the hob requires a 4mm cable supported by a minimum 32a fuse as the hob is 6500w. How can I do this??

Any help appreciated.
 
Prepare to upset your client by telling them it needs a new feed, disturbing all that lovely new plaster!

Had this done to me a couple of times, why do people not make decisions at the right time??!
mate....you need to think a little before posting this kind of thing...
as has been said already here...diversity...
someone may take this as gospel...and make work for nowt....and possibly lose further custom through it....
 
One reason why on almost every kitchen rewire, i fit a twin 1 gang back box. 1 side can be used for a cooker connection plate and the other a single socket or FCU. Covers all outcomes then.

Rewiring the circuit, are you on drugs or what
 
Surly you would be alright on a 32 after applying diversity -10 amps then -30% depends on the client tho that's just a general guide

For the Umpteenth time, A cooker (be it a combined all in one appliance or oven and hob set-up) up to 15 KW is perfectly good on 6mm cable with a 32A MCB/RCBO OCPD (or pre metric, ...7/044/30A OCPD)!! And has been for well over 60 odd years !!
 
doing kitchen upgrade oven was already wired in 10mm all ok new oven and micro oven wired off switch giving me 6100watt with out diversty problem being oven and micro oven pre wired in 1.5 flex. flex cannot be replaced will this be compliant on a 32amp mcb as it was wired when i came to fit two seprate loads from one cooker switch one to micro oven one to main oven would this be ok as it would only be pulling load of the micro oven through that flex and not pulling the load off oven not pulinng the load off both through flex if both on. flex lenght less than three meters. will be nite mare to run new circuit for micro oven i know two oven meant to be on two switches everything plastered and painted.
 
doing kitchen upgrade oven was already wired in 10mm all ok new oven and micro oven wired off switch giving me 6100watt with out diversty problem being oven and micro oven pre wired in 1.5 flex. flex cannot be replaced will this be compliant on a 32amp mcb as it was wired when i came to fit two seprate loads from one cooker switch one to micro oven one to main oven would this be ok as it would only be pulling load of the micro oven through that flex and not pulling the load off oven not pulinng the load off both through flex if both on. flex lenght less than three meters. will be nite mare to run new circuit for micro oven i know two oven meant to be on two switches everything plastered and painted.

casn you fit 2 x 13A FCUs for the 2 flexed appliances?
 
was thinking about that but but one oven is 3500 watt which would give over 13 amp and micro oven states that 15 amp supply required trying to make best out off bad situation may go with 13amp fcus but dont want them to blow behind cookers once in place i dont know why the manufacturers dont up rate the flex to suit power demand because it pretty much on the limit was going to just up rate the flex as this cant be done may have to fit fcu or lower the mcb to 20 amps which could cause to trip even after diversty is applied but this mite be better than fuses blowing behind aplliances
 

Reply to Cooker and hob in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
183
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
560
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
516

Similar threads

  • Question
Thank you for fast response. The reason I asked is because I had read elsewhere online: "Electric ovens have a wattage rating that tells you how...
Replies
2
Views
1K
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top