i "nearly" understand the diversity calc, first 10a plus 30% of remainder, i just can not get my head around how 6mm cable and a 40a mcb is adequate for this size of cooker when if you installed a 10.5kw shower it wouldn't be.
thats because when you install a shower there is no ,,,, diversity allowed.....but in a cooker there is....that why see....lol...
 
But i agree that manufacturers should in this day and age state maximum KW loading, rather than the connected KW load.... As a 17KW cooker isn't really 17KW, it's more like a 15 or 15.5KW cooker....

e54... If you apply the basics of the cooker diversity of first 10a plus 30% of remainder, have i got this right...??

17.1kw = 74.35a
10a + 30% of 64.35a = 29.3a

So, the circuit you install must be designed for 29.3a = 6.7kw ??
 
But i agree that manufacturers should in this day and age state maximum KW loading, rather than the connected KW load.... As a 17KW cooker isn't really 17KW, it's more like a 15 or 15.5KW cooker....

e54... If you apply the basics of the cooker diversity of first 10a plus 30% of remainder, have i got this right...??

17.1kw = 74.35a
10a + 30% of 64.35a = 29.3a

So, the circuit you install must be designed for 29.3a = 6.7kw ??

it's worked for 60 odd years. no reason to think any different today. best thing is in the proof of the pudding, as they say. switch everything on and clamp meter it. initial current might be a little bit over, but bet it settles down to no more than 30(ish) amps.
 
So why dont the manufacturers just call it a 7kw oven and do away with the diversity... Would make a lot more sense, as the manufacturers would know exactly what the oven can draw at any one time.
 
they can't do that, because then nobody would buy them. what customer would think of buying an oven less powerful than mrs. jones at no.47.
 
it's worked for 60 odd years. no reason to think any different today. best thing is in the proof of the pudding, as they say. switch everything on and clamp meter it. initial current might be a little bit over, but bet it settles down to no more than 30(ish) amps.

I totally agree with you but i get customer saying to me that the spur off a spur off a spur has been fine for 30 years and there not much chance of much being overload as they dont really use them anyway. what do u say when you say u only need 6mm for cooker because its been fine for 60 years
 
Can't see a problem for you Jimmyb, if they want you to install a 10mm cable when a 6mm will be adequate, then rub your hands together and provide them the 10mm!! And the extra cost...lol!! ....Simples!!!!
 
@ jimmyb. when i said it's been fine for years, i meant also that it's compliant with regs. as well.
 
totally agree with you telectrix.

I wasnt referring to the cooker circuit and beside if they install a 10mm instead of 6mm how im i going to make much if any because it will take about the same time so unless im going to rip people off which i anit it doesnt make much difference, I was talking about the spur off a spur off a spur
 

Reply to Cooker cable sizing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
164
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
Thanks for replying
2
Replies
23
Views
2K
Although it might appear that I am being elusive with the facts, the point is, only you know what your worth is per hour and how long it will...
    • Optimistic
Replies
3
Views
464

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top