Question from a 2400 paper
Cooker @ 12000w. TN-C-S @ Ze= 0.25ohms. Socket on cooker switch. BS1361 fuse. 25 meter run.
PVC t&e clipped direct with 4 other cables. Passes through 100mm length of surrounded insulation. Leaves group and in HG pvc conduit in ambient of 45 degrees.
Ib = 52amps diversity - 10+(30% of remaining 42A)+5 for socket = 28 Amps
In = 30A fuse
Correction factors Cg= 0.65 (4 cables... or should this be 5 to include this cable?)
Ca= 0.81 and Ci= 0.75
Worst 2 = Cg x Ci = 0.507 (or do we use all three?)
30 / 0.507 = 59.17 Amps to be carried
Cable selected is 10mm with tab ccc of 64 Amps - 4mm cpc
4.4mV x 28 x 25 = 3.08 volts so ok as <11.5v
Zs = 0.25 + ((6.44) x (1.2 group x 1.18 ambient)) = 0.477 ohms
adiabatic I get 1.32mm
Can anyone point out where I may have made a mistake, any pointers or if I've got this right, please?
Thanks in advance - s.f
Cooker @ 12000w. TN-C-S @ Ze= 0.25ohms. Socket on cooker switch. BS1361 fuse. 25 meter run.
PVC t&e clipped direct with 4 other cables. Passes through 100mm length of surrounded insulation. Leaves group and in HG pvc conduit in ambient of 45 degrees.
Ib = 52amps diversity - 10+(30% of remaining 42A)+5 for socket = 28 Amps
In = 30A fuse
Correction factors Cg= 0.65 (4 cables... or should this be 5 to include this cable?)
Ca= 0.81 and Ci= 0.75
Worst 2 = Cg x Ci = 0.507 (or do we use all three?)
30 / 0.507 = 59.17 Amps to be carried
Cable selected is 10mm with tab ccc of 64 Amps - 4mm cpc
4.4mV x 28 x 25 = 3.08 volts so ok as <11.5v
Zs = 0.25 + ((6.44) x (1.2 group x 1.18 ambient)) = 0.477 ohms
adiabatic I get 1.32mm
Can anyone point out where I may have made a mistake, any pointers or if I've got this right, please?
Thanks in advance - s.f