Hi

Step 1: Ib = 12000/240 = 50A, diversity 10A + (30% of 40A) + 5A = 27A
So Ib = 27A

Step 2: In = 30A

Step3: I'd say in conduit and at an ambient of 45deg. I would not use any Cg or Ci figures as the worst factor compensates for them, this is done when there are combination of factors not all affected at the same time.

Ca = 0.79
Cg = 1
Ci = 1
30/0.79*1*1 = 38A

Step 4: Cable selected is 6mm with 4mm cpc using Ref Method B as the conduit is in the roof space not in an insulated wall! Therefore CCC of 41A.

Step 5: 7.3mV*27*25 = 4.93V = 2.05%

Step 6: Maximum Zs for 30A BS1361 is 1.15 ohms
R1 = 0.08
R2 = 0.12
ZS = 0.25 + ((0.08*0.12)*1.2) = 0.49 ohms

Step 7: csa = 2.74mm so the cpc complies.

I know this is an old subject but i think the calcs are fine but have noticed a few mistakes ( or I could be reading it wrong, if so sorry )

In step 3 the wost case would be the grouping factors as that is 0.60 ( 5 cables together) so
30/.60*1*1=50A

So step 4 would be select a cable of 10mm with a 6mm cpc from TABLE 4D2A, method C clipped direct........... Not sure if i'm right.............please can anyone tell me??
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Cooker calc
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
silva.foxx,
Last reply from
rob1967,
Replies
15
Views
3,559

Advert

Back
Top