Evening all.
Customer needs a new oven and electric hob. The current setup is 6mm T+E on 32A MCB, RCD protected, about 8M run, reference method 100. The oven they are looking at is 10.5KW. I initially thought that was too much but after adding diversity it seems ok. Are my calculations ok as I want to check.
My calculations are
10.5KW = 45.64A.
So 10A + 10.69A (30% of remainder f.l) with no socket = 20.69A
Think ive done everything right just seems 45A down to 20A is a big jump.
Does this sound ok.
Thanks in advance.