Just finishing a rewire, customer not sure on hob and cooker at design stage so I went for 2 circuits with 6mm withe 2 32amp rcbo's. Hob and cooker 5 meters apart. Now induction hob and oven have arrived onsite and both suggest a 13amp supply is suffice. Should I downgrade the rcbo's to 16amp and hard wire into plate or exchange plate for non switched fused spur and leave rcbo as is
 
[ElectriciansForums.net] Cooker circuit options
 
Just finishing a rewire, customer not sure on hob and cooker at design stage so I went for 2 circuits with 6mm withe 2 32amp rcbo's. Hob and cooker 5 meters apart. Now induction hob and oven have arrived onsite and both suggest a 13amp supply is suffice. Should I downgrade the rcbo's to 16amp and hard wire into plate or exchange plate for non switched fused spur and leave rcbo as is

Single oven will be ok.Customer has bought the wrong hob. 13A induction has to load share to work with such limited capacity. They should have bought the full blown 7Kw + model. They will hate what they've bought as soon as they use more than one hob lol.
As said above, leave the 32A RCBO's place and Spurs or plugtops will be ok.
 
How on earth are they going to void a warranty?

Are you referring to that utter nonsense about removing a moulded plug voiding the warranty on a whole appliance?

That’s not quite true. I got simarly lambasted a few years ago on this very subject, and so did some ‘extensive’ research for myself. :)

Most of the manufacturers don’t give a hoot if you cut their moulded plugs off. However, I did find one or two that did. There were also some that required their original lead replaced, with an manufacturers one, if that is damaged.

Unfortunately, I never retain my research, so can’t tell you who was being a bit fussy. But recommend you read the instructions before getting out your snips.
 
At the end of the day the manufacturer's warranty is in addition to your legal rights. Your legal rights won't be affected by removing the plug. Your legal rights extend to six years as against the manufacturer's typical one year.
 
I knew as soon as the word 'plugtop' was mentioned that George would be along. Any how, must dash as I need some MR16 bulbs.
don't be silly, you plant them in february/march. use the money for beer.
 

Reply to Cooker circuit options in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
701
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top