Hi All, First post for me so be kind out there.
Your comments would be appreciated.
Doing a periodic/EICR on a rented house and found new kitchen fitted, old cooker circuit was terminated into JB on top of units and ring circuit taken from here by 2X 2.5 cables to feed 4 sockets and boiler spur in kitchen.
ZS measured at .65.
No electric cooker in kitchen now.
MCB 32A bit unconvential but whats wrong with it?
Thanks..
Your comments would be appreciated.