Hi all, I was wondering if anyone had any advice or put me right, im to wire a hob that's 6 kw and Elec oven 4.25 kw,would I be right in saying that a 45 amp breaker, with a 10mm cable suppling both hob and oven via Dual appliance out let plate. Would this be adequate, any help guys would be appreciated
 
The reason I'm thinking 10 mm is the fact that the kit fitter who I have never met has orderd this oven, I have not seen oven yet, he advised me of kw ratings and amps per appliance,

Such is the power of this new fangled internet thingy, that one can download instructions from manufacturers websites these days!! WOW.
 
You must follow the Manufacturer's Instructions or it will not comply.

Manufacturers instructions of cookers and the like, have in the most part been misleading for as far back as i can remember. They only ever state connected load, whether those loads can be operated at the same time or not, and make no allowances for the thermostatic functioning of elements...

The diversity factor as outlined in BS7671 has been in use for over 50 years, because it Works.
 
Actually it does have something to do with diversity, as your supposedly very important MI's only give connected load ratings, and as we know, they bare very little relationship in the real world...

But then again i guess, you will still carry on supplying two Radial circuits, or an over-sized cable at the customers expense, for no other reason other than ....That's what was in the MI !!!
 
You're missing the point - thank you for your completely unfounded insult, I shall assume you misread - I am arguing the other way around.

The MI for the oven state 20A. Therefore it will supposedly come with a 20A flex. The OP is talking about having this on a 45A mcb (later he may change to 32A).

Either way this is unsatisfactory.
 
I'm not fully upto date with the regs but with a good few years in the game I've found it pays to keep things simple, then charge accordingly.
Logic and useability would suggest a supply for each appliance rated according to the plate on the appliance, all bases covered that way.
That way if one goes belly up the housholder can still use the other appliance.
For me its nothing to do with regs, maths or cost, its just common sense.
 

Reply to Cooker circuit in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
270
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
685
I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
427

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top