Gringoking88

-
DIY
Joined
Jun 18, 2015
Messages
176
Reaction score
58
Location
London
Hi all,

I have just been to a job where the existing hob is wired in using 2.5mm heat resistant cable, the hob is rated at 6000w. I calculate this to need a 4mm cable, however, was challenged by someone, in the end I called NICEIC who stayed neutral and said it "might be ok, what do the instructions say" instructions dont specify the cable size needed.

What size cable would you guys use?

Many thanks in advance,

M
 
6000/230=26A

Diversity: read Appendix A in your OSG, and the allowance for cookers is in table A1. This will give you your design current for the circuit. Come back to us with that.

Hang on, there's an oven on it as well?
Yes there is a 13 amp oven. I understand the diversity part e.g. first 10 amp plus 30% of the remainder, however, the circuit is pre existing, I am referring to the cable literally the connection point to the hob.
 
Yes there is a 13 amp oven. I understand the diversity part e.g. first 10 amp plus 30% of the remainder, however, the circuit is pre existing, I am referring to the cable literally the connection point to the hob.
Oh and there is a socket so rated current is
What do the manufacturers instructions say?
They dont, they just specify the heat resistant cable and not the actual size, I called them (Zanussi) and they said they didnt know and to email in.
 
Ah I see. I presume ref method C?

From about P400 of the BS7671 you'll find the tables for current carrying capacity for various cables. Yours would be 2.5mm, multicore, presumably 90deg if it's heat resistant, and it's not armoured. Have a butchers and tell us the CCC for your cable
 
Ah I see. I presume ref method C?

From about P400 of the BS7671 you'll find the tables for current carrying capacity for various cables. Yours would be 2.5mm, multicore, presumably 90deg if it's heat resistant, and it's not armoured. Have a butchers and tell us the CCC for your cable
26 amp when in free air. I guess that answers the question, but is very close to the mark.
 

Reply to Cooker connection unit to hob cable size in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
315
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
954

Similar threads

  • Question
I actually did it with a 4 core 4.0mm swa last week!
Replies
12
Views
786
  • Question
Thanks for replying
2
Replies
23
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top