FYI with regards to placing FCU beyond the point of cable reduction:
434.2.1 Except where Regulation 434.2.2 or 434.3 applies, a device for protection against fault current may
be installed other than as specified in Regulation 434.2, under the following conditions:
In the part of the conductor between the point of reduction of cross-sectional area or other change and the position
of the protective device there shall be no branch circuits or socket-outlets and that part of the conductor shall:
(i) not exceed 3 m in length, and
(ii) be installed in such a manner as to reduce the risk of fault to a minimum, and
NOTE: This condition may be obtained, for example, by reinforcing the protection of the wiring against external
influences.
(iii) be installed in such a manner as to reduce to a minimum the risk of fire or danger to persons.
Length and.... protection from damage need to be considered as damage to the cable after the CSA reduction but before the fuse, the fault current will over load the cable before the main protective device trips?
Open to correction