Don't know if anyone else has asked, and my head hurts when I try to read back through the posts, but these 3 Electricians that have looked at your problem, did they leave any reportsafter they hAD
No, I don't think so, sorry.
Don't know if anyone else has asked, and my head hurts when I try to read back through the posts, but these 3 Electricians that have looked at your problem, did they leave any reportsafter they hAD
OP from what you've described, your faulty (possibly) cooker hood is tripping circuits 5 or 6, when logic suggests it should be tripping circuit 4, i.e. kitchen sockets? Unless the kitchen fitter, pinched a supply from the upstairs ring to feed the cooker hood?
Think the sparking hob thing is artistic licence, and too much wine when cooking
You could unplug your cooker hood temporarily, and see if that stops the fault.
Why don't you first try disconnecting the cooker hood by turning off at the wall switch you mention. This should be a double pole switch, which should electrically disconnect it from it's supply. If the fault not longer manifest itself, then you could start looking at having the appliance tested for faults.
This does not explain why the hood on circuit 4, is tripping circuits 5 & 6. Sometimes with the best or worse intentions, kitchen fitters deputise themselves as electricians, and can make a right hash of things, this of course is not true of all kitchen fitter electricians. If, as it already has been suggested, these circuits have been cross connected, may be one possible line of inspection.
I note that your fuse board is populated with MEM ALB321 mcb's. I don't believe you could purchase an MEM ALB321 RCBO (Residual Current Breaker with Overcurrent)? You can however, I'm told, convert them to an RCBO, using a field fit RCD Pod. MEM are no more, but spares are obtainable from EATON, well not spares but replacements. Clutching at straws, perhaps these kits have not be assembled as per manufacturers instructions?
You seem to have some confidence & trust in the electrician who originally rewired your property. Why don't you see if he/she will come back and investigate these faults?
It is difficult to carry out fault finding from afar. The label on your fuse board suggest you are due an inspection anyway.![]()
Fair comment. It's just that after having had 3 competent* local sparks draw blanks I thought I'd try a different tack for some input. Which I've gotYou won't diagnose and fix this on a forum. You need a competent local spark with time, a mft and a clamp. Meter......
And money to pay them
P.s. I'm sure those are rcbo's
so some match making - Tom are you in Oxford? Midwest - how close are you to Oxford?
so some match making - Tom are you in Oxford? Midwest - how close are you to Oxford?
Because each circuit you have is individually protected by an RCBO an earth fault on one circuit cannot affect another circuit.
However it is slightly possible, especially as the board is quite old, that the RCD portion of perhaps both circuits 5 and 6 is becoming damaged and perhaps sensitive to voltage transients, which could be generated by the cooker hood and possibly by the ignitor.
I would more probably expect that the problem is more related to a fault on one or both of the socket circuits or weak RCDs.
A potential sense check might be to get an electrician to initially test if the RCBOs function correctly and secondly to swap the RCBOs between circuits and see if the fault follows the RCBO or not.
Obviously if the tripping remains with the RCBO then the RCBO should be changed, however it would have to be a secondhand one as they are no longer available.
If the fault does not follow the RCBO but remains with the circuit then the concentration should be on testing the circuits for, probably, neutral earth faults either internally to the circuit or between circuits 5 and 6.
Yes, Midwest, are you within reach of Kidlington? I trust my original electrician but it would be good to get another pair of eyes to have a look...
Okay, will do, Midwest.PM me if your original electrician can't assist. Bear in mind if the RCBO's are defective as Richard suggested, their replacements are about £80 each. Hopefully your electrician might just find a simple fault with the wiring.
Is the trip random or cab you make it do it?
Not sure what your point is, sorry...But you are reporting that a device on circuit A is tripping circuits B and C - which shouldn't happen.
The post that you linked to is describing a fault that trips the RCBO to which the circuit is connected. Your fault is tripping an unrelated RCBO so the fault resolution will be different.Not sure what your point is, sorry...![]()
Sure, I just thought any information might be useful. I was answering the question of whether I can repeat the fault at will. Even if the fault resolution is different, I thought the information about the fan speed adjustment might be helpful in working out why the fan causes anything to trip. To my (admittedly layman's) mind, why the fan causes a trip and why those particular circuits get tripped are the two elements of this puzzle.The post that you linked to is describing a fault that trips the RCBO to which the circuit is connected. Your fault is tripping an unrelated RCBO so the fault resolution will be different.
Though it is possible that the fault on the socket circuits allows the same effect to occur, just through a fault rather than directly on the circuit, but a bit unlikely.
Yes, I think you're probably right.I think you should give up with internet advice and get your wallet out
It could be by crossed earths in the split load consumer unit.
Crossed earths?It could be by crossed earths in the split load consumer unit.
It could be by crossed earths in the split load consumer unit.