Morning all,

I'm Having an issue with a cooker install and wonder if anyone can help.
Every time the cooker is switched on there is a RCCB trip (Rated at 80a 30Ma). The circuit will take a supply but no load of any kind. I connected a DeWalt charger to the socket on the cooker plate (only drawing 0.85a) and it still trips. The rest of the ring main/lighting circuit has no issues and tests with no problems.

Testing path -
Tested appliances, all good.
New cable run, thought it may be a neg earth fault due to a rogue screw/nail so replaced the cable again.
Removed all other connections in the distribution board so only the cooker was connected, same problem.
Swapped out the 40a breaker.
Swapped out the cooker connection plate.
All polarity & resistance checks out.

Scratching my head here, any help would be appreciated.

Thanks,
D
 
Morning all,

I'm Having an issue with a cooker install and wonder if anyone can help.
Every time the cooker is switched on there is a RCCB trip (Rated at 80a 30Ma). The circuit will take a supply but no load of any kind. I connected a DeWalt charger to the socket on the cooker plate (only drawing 0.85a) and it still trips. The rest of the ring main/lighting circuit has no issues and tests with no problems.

Testing path -
Tested appliances, all good.
New cable run, thought it may be a neg earth fault due to a rogue screw/nail so replaced the cable again.
Removed all other connections in the distribution board so only the cooker was connected, same problem.
Swapped out the 40a breaker.
Swapped out the cooker connection plate.
All polarity & resistance checks out.

Scratching my head here, any help would be appreciated.

Thanks,
D
When you say all Polarity and Resistance checks OK what where the IR readings? and was the cooker ON when you tested L to E and N to E, and at what voltage setting did you use on your MFT
 
Morning all,

I'm Having an issue with a cooker install and wonder if anyone can help.
Every time the cooker is switched on there is a RCCB trip (Rated at 80a 30Ma). The circuit will take a supply but no load of any kind. I connected a DeWalt charger to the socket on the cooker plate (only drawing 0.85a) and it still trips. The rest of the ring main/lighting circuit has no issues and tests with no problems.

Testing path -
Tested appliances, all good.
New cable run, thought it may be a neg earth fault due to a rogue screw/nail so replaced the cable again.
Removed all other connections in the distribution board so only the cooker was connected, same problem.
Swapped out the 40a breaker.
Swapped out the cooker connection plate.
All polarity & resistance checks out.

Scratching my head here, any help would be appreciated.

Thanks,
D
you have replaced the cable again .so did you not do ir on the circuit to see which leg was giving a fault .
 
Sounds like a faulty RCCB.
Oh yes, lets change everything. RCCB, cable, cooker, isolation switch, etc:eek:
Probably there will be the same result.

What is needed is a change in the level of competence.
 

Reply to Cooker install - RCCB tripping in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

  • Question
Since my last post I have used the oven several times and it is still working ! On reading the 'regulatory' position I will ask an electrician to...
Replies
9
Views
2K
Thanks all for the suggestions! Customer doesn't store anything else in the cupboard with the tank, not even towels or sheets. Heatrae stat is...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top