Morning all,

I'm Having an issue with a cooker install and wonder if anyone can help.
Every time the cooker is switched on there is a RCCB trip (Rated at 80a 30Ma). The circuit will take a supply but no load of any kind. I connected a DeWalt charger to the socket on the cooker plate (only drawing 0.85a) and it still trips. The rest of the ring main/lighting circuit has no issues and tests with no problems.

Testing path -
Tested appliances, all good.
New cable run, thought it may be a neg earth fault due to a rogue screw/nail so replaced the cable again.
Removed all other connections in the distribution board so only the cooker was connected, same problem.
Swapped out the 40a breaker.
Swapped out the cooker connection plate.
All polarity & resistance checks out.

Scratching my head here, any help would be appreciated.

Thanks,
D
 
Reminds me of a time I was out in Bath with a load of work mates, all out on the lash going round a few bars then off for something to eat. About to go into the sixth or seventh bar when I noticed my boot was undone, used the door step to rest on while doing up the lace. As I looked up there was a nice brass door sign "welcome to Mandalays Baths Premier Gay Bar" ! Super funny as they all filed out passed me calling me several names for not telling them. Truth is I just stopped to do up my shoe ! The bar man, fair play to him had checked they where in the right pub before taking the beer orders.
Sooooo outside a gay bar bent over pretending to tie up your boot laces......... and you think we'll believe that one......
 
Morning all,

I'm Having an issue with a cooker install and wonder if anyone can help.
Every time the cooker is switched on there is a RCCB trip (Rated at 80a 30Ma). The circuit will take a supply but no load of any kind. I connected a DeWalt charger to the socket on the cooker plate (only drawing 0.85a) and it still trips. The rest of the ring main/lighting circuit has no issues and tests with no problems.

Testing path -
Tested appliances, all good.
New cable run, thought it may be a neg earth fault due to a rogue screw/nail so replaced the cable again.
Removed all other connections in the distribution board so only the cooker was connected, same problem.
Swapped out the 40a breaker.
Swapped out the cooker connection plate.
All polarity & resistance checks out.

Scratching my head here, any help would be appreciated.

Thanks,
D

The test first would have been better to eliminate a cable fault !!! Have you charged someone for the time of doing this??
 

Reply to Cooker install - RCCB tripping in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
813
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

  • Question
Since my last post I have used the oven several times and it is still working ! On reading the 'regulatory' position I will ask an electrician to...
Replies
9
Views
2K
Thanks all for the suggestions! Customer doesn't store anything else in the cupboard with the tank, not even towels or sheets. Heatrae stat is...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top