Thanks Jock. Hadn't heard of continuity test. I wondered if it might be the wire being nipped by screws on new kitchen Units. The house also had a rat in it during covid. It had an electric safety check and the electrician tested the cooker circuit with high voltage meter. He says that woukd show any weakness in the cable. If it's not the cooker, the cable or the breaker, could it be anything else?
It would show weakness in the insulation ,the neutral or live could be hanging by a thread if something has damaged it
 
I gave him the make and model of cooker. He said the total amps was 35. That's why he changed from 32 to 40.
Total amps is 35 but you would normally allow for diversity .10 amps of total load plus 30 percent of remaining load.a 32 amp would normally work fine with that unless the cooker is being used to heat the room or being used all at once every time being used which is highly unlikely.is there a socket on cooker switch if so add another 5 amps on to calculation
 
Total amps is 35 but you would normally allow for diversity .10 amps of total load plus 30 percent of remaining load.a 32 amp would normally work fine with that unless the cooker is being used to heat the room or being used all at once every time being used which is highly unlikely.is there a socket on cooker switch if so add another 5 amps on to calculation
It might be being used all at once. I have seen the tenants cooking and all hobs and both ovens were on.
 
It might be being used all at once. I have seen the tenants cooking and all hobs and both ovens were on.
Even then cookers work in a way that thermostatically all the rings and oven are never on at same time ,maybe for 1 minute or so .plus a 32 amp mcb wouldn't overload at 35 amps .plus most cookers nowadays will give you total load but for instance you can't have grill and oven on at same time.i really don't think that's your problem.see what your electrician comes back with when he does his continuity tests
Assuming 35 amps hasn't been flowing thru mcb for a considerable amount of time
 
Even then cookers work in a way that thermostatically all the rings and oven are never on at same time ,maybe for 1 minute or so .plus a 32 amp mcb wouldn't overload at 35 amps .plus most cookers nowadays will give you total load but for instance you can't have grill and oven on at same time.i really don't think that's your problem.see what your electrician comes back with when he does his continuity tests
Thanks Jock. Appreciate your help
 
No worries. Hope you get it sorted
Hi Jock. These are images of the breaker. The cooker is the smudged writing. It seems that it will trip with just 1 hob on for a period. Thanks
 

Attachments

  • [ElectriciansForums.net] Cooker tripping
    20241216_175443.jpg
    829.3 KB · Views: 21
  • [ElectriciansForums.net] Cooker tripping
    20241216_175450.jpg
    767.1 KB · Views: 21
Hi Jock. These are images of the breaker. The cooker is the smudged writing. It seems that it will trip with just 1 hob on for a period. Thanks
Thanks.because it's a combined mcb and rcd [rcbo] it could be tripping due to a neutral fault .if the cookers new then each part of the circuit would need to be tested and tested with cooker cable removed from rcbo ,switch would need to be disconnected as well as cooker outlets.check for plate screws incase it's nipped a neutral or live ,it's easy done.also if it's metal boxes check for grommets in back boxes ,make sure no basic insulation is touching or even close to metal knockouts . At furthest point in circuit check for any voltage on neutral wire this should be close to zero , .it should be easy to identify using a low reading ohm metre [a multi function tester] connect the live and earth together at consumer unit and then test between live and earth at cooker switch ,take note of result.repeat the process with the neutral, the results should be exactly the same say 0.12 ohms.do this with every part of circuit ,switch down to cooker out let [if there is one ] is it a free standing cooker or is there a separate hob and oven on same circuit/switch maybe the oven is the problem ..when your happy with readings then you can do a insulation resistance test on each part of circuit .be carefull that your cables are removed from rcbo ,switch neon if there is one and most important cooker oven . Then test between live to earth ,live to neutral and neutral to earth .you can do this at 250 volts .it could also be an issue with another circuit possibly.make sure your electrician does this as he will have the proper tester and safety equipment
Hi Jock. These are images of the breaker. The cooker is the smudged writing. It seems that it will trip with just 1 hob on for a period. Thanks
 
Last edited:
Thanks.because it's a combined mcb and rcd [rcbo] it could be tripping due to a neutral fault .if the cookers new then each part of the circuit would need to be tested and tested with cooker cable removed from rcbo ,switch would need to be disconnected as well as cooker outlets.check for plate screws incase it's nipped a neutral or live ,it's easy done.also if it's metal boxes check for grommets in back boxes ,make sure no basic insulation is touching or even close to metal knockouts . At furthest point in circuit check for any voltage on neutral wire this should be close to zero , .it should be easy to identify using a low reading ohm metre [a multi function tester] connect the live and earth together at consumer unit and then test between live and earth at cooker switch ,take note of result.repeat the process with the neutral, the results should be exactly the same say 0.12 ohms.do this with every part of circuit ,switch down to cooker out let [if there is one ] is it a free standing cooker or is there a separate hob and oven on same circuit/switch maybe the oven is the problem ..when your happy with readings then you can do a insulation resistance test on each part of circuit .be carefull that your cables are removed from rcbo ,switch neon if there is one and most important cooker oven . Then test between live to earth ,live to neutral and neutral to earth .you can do this at 250 volts .it could also be an issue with another circuit possibly.make sure your electrician does this as he will have the proper tester and safety equipment
Fantastic Jock. Thankyou
 
Hi Jock. These are images of the breaker. The cooker is the smudged writing. It seems that it will trip with just 1 hob on for a period. Thanks
The picture on the left shows a blank missing on the far left.
This is very dangerous.
Do not put your fingers in that hole.
You need to get an electrician to put a blank there immediately.
 

Reply to Cooker tripping in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
673
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

T
The gas hob might still need to be plugged in for the ignition, but an electric oven should have its own supply. You may need to employ the...
Replies
4
Views
303
Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
774

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top