Hi, i have built a log cabin and now routing cabling. I want to do this on the outside as it looks better. Can i ask if i can safely use the conduit from toolstation, here... 25mm Heavy Duty Round PVC Conduit - https://www.toolstation.com/25mm-heavy-duty-round-pvc-conduit/p66251

It has to be signed off by an electrician and from my research must be IP54 atleast. Is this correct? The conduit linked above has no IP rating, only the flex conduit does. Which is fine if i have to use that. The junction boxes don't seem to have a IP rating so now trying to understand what to use.


Is it a case of purchasing the rubber gaskets and this then makes it IP54 or above?

Apologies for the daft question and appreciated any help.
 
Products that have an IP rating are certified as a single assembled unit. Conduit and accessories will be put together by whoever (you in this case). So the resulting resistance to any external influence will be down to the quality of your expertise!

I'm guessing that this work will require notification(?). Certainly it will need to be certified.
Please don't tell us that you plan to do the work and then try and find some unsuspecting electrician to come and "sign it off".
you need to get your electrcian in BEFORE YOU START.
 
  • Like
Reactions: MDJ
No unsuspecting Electrician, he is aware. My friend is a sparky but hasnt kept up with his certification to sign things off. However his colleague is an electrician and happy to come and do it.
Im just trying to do as much work as possible for him. ie routing cables etc so he can then come in and get on.

I can of course pester him with my Q but thought i wouldn't need to by asking the Q on a forum. Happy to research myself etc
 
Basically, PVC cables are waterproof. The place you need no water -in conduits- is where there are cable junctions.
Also, if you run your conduit outside, then any water that gets into the conduit will run to the lowest point, and that may be the hole through and into your cabin.
 
Apologies so going back to my original Q, i can use that conduit but have to ensure the connections to junction boxes are sealed in some way? ie using gaskets and maybe sealant on the actual joins?
 
Hi, i have built a log cabin and now routing cabling. I want to do this on the outside as it looks better.
It will look a pigs ear and after 1 winter and 1 summer will be buckled and twisted and be all over the place lol
 
Hi, i have built a log cabin and now routing cabling. I want to do this on the outside as it looks better. Can i ask if i can safely use the conduit from toolstation, here... 25mm Heavy Duty Round PVC Conduit - https://www.toolstation.com/25mm-heavy-duty-round-pvc-conduit/p66251

It has to be signed off by an electrician and from my research must be IP54 atleast. Is this correct? The conduit linked above has no IP rating, only the flex conduit does. Which is fine if i have to use that. The junction boxes don't seem to have a IP rating so now trying to understand what to use.


Is it a case of purchasing the rubber gaskets and this then makes it IP54 or above?

Apologies for the daft question and appreciated any help.
Do you mean like this :
View: https://www.youtube.com/watch?v=bOmE0lx2c5M


Internal wiring is definitely going to give more longevity.
 

Reply to Correct Conduit Assistance in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

It’s fine.. bit awkward to install in conduit especially LSOH 2.5mm T&E
Replies
3
Views
1K
Hi, folks.' I have a carrier 38MGRQ48E '5 zone' mini split system with 4 'heads'/evaporators installed, and one 'channel' still open. Had it...
Replies
0
Views
969
Hello, I’ve have some ten year old Collingwood SL020 RGB led garden spike lights which I’d like to keep using but wondering if I can use them with...
Replies
0
Views
873
  • Question
Yes I still use a Robin makes the young lads jump when the leads crack on the terminals plus no batteries to go flat.
2
Replies
29
Views
5K
  • Question
How long is the conduit????
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks