See attached photo of my new 3 phase supply at my house. Tails supply a Schneider 3ph board. Sparky is in two minds about the correct earthing method as the powergrid haven't supplied an earth. What's the correct method?

[ElectriciansForums.net] Correct earthing method for house?
 
I would ask the supplier why they didn't supply a earth, it looks like you may have to TT the system, but the Electrician should at least enquire about this, also the earth at the bottom looks pretty small so I am assuming it goes to a rod and not the DB, My eyes are not great these days mind but the earth is 6mm2 at best to my eyes
 
As MDJ said. The DNO are not obliged to supply an earth, they normally do but sometimes they don't if they think their system is not suitable or if they think the installation is not suitable for TNCS.
 
Looks like there's phase reversal going on there as well to correct (one hopes) miswired conductors inside the head??
 
Is this a new installation as pencilled labels behind tails from cutout - R Y R N?? Usually marked - L1,L2,L3+N (SSE do).
I spotted that as well and wondered what that is all about - R Y B, maybe, if the fitter was proper old school, but that makes no sense at all.
 
To the OP, I would ask the sparky to measure the "Ze" using the neutral and a phase.

If it comes out low at 0.35ohm or so, then ask the utility for the earth - most are trying to deliver PME when they can, so might be an oversight.

If it comes out much higher then this that would be why they didn't provide an earth (they aren't actually obliged to do so), so clearly a earth has to be provided by the sparky meaning a TT system, in which case the sparky may need to redesign parts of the installation.
 

Reply to Correct earthing method for house? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
707
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
502
I tend to write the circuit number on the mcb say every 5th mcb/rcbo just to help make it easier to locate in a large multi way or 3ph board...
2
Replies
17
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top