srl-8

Hello guys. I am new on here and wanted to get involved.
Firstly, I am on route to becoming a domestic installer and now becoming very inquizitive when I see other peoples installations.. And for the record, I know i have a LONG way to go before I would consided myself competent !

At my parents house, they have had a new electric shower put in, but I am unsure if the electrican has used the correct rated MBC...Can someone clarify the below

Taken a new feed from the Hendy Block and feed a Small 2 way C/u (Just for the bathroom)
The new Cu has a 63A / 30ma RCD main switch, and then 6A MCB and a 32 A MCB which the shower is on.
The shower Cable is 10mm.
The shower is rated at 9.8kw / 9800 watts

I think this MCB is underated and should be a 45A MBC, however it have never tripped??

Can someone explain what is happening here

Thanks!!

SRL-8
 
A 32A B type MCB will run at 38A for ever, so it will cope with 42.6A for average shower use, which is why it has not tripped.


Although shower manufacturers go for a continuous rating for MCB ratings, a lot of showers do not have a continuous duty rating, many are just 20min on 20min off, or variations of that but that is hidden away in the instructions.

In which case a 40A MCB will do even at the lower end of the supply voltage when the current drawn by the shower will be 47.3A, insulation derating factors and installation methods, then start to become a problem!

 
A 32A B type MCB will run at 38A for ever, so it will cope with 42.6A for average shower use, which is why it has not tripped.


Although shower manufacturers go for a continuous rating for MCB ratings, a lot of showers do not have a continuous duty rating, many are just 20min on 20min off, or variations of that but that is hidden away in the instructions.

In which case a 40A MCB will do even at the lower end of the supply voltage when the current drawn by the shower will be 47.3A, insulation derating factors and installation methods, then start to become a problem!



Not according to ABB whose low current test on page 14 on their data sheet is 1.13 In. Which would make a Type B 32amp MCB trip at just over 36amp on continuous load. But a shower that is on for less than an hour will not trip the MCB as the high current rating is In X 1.45.

http://www05.abb.com/global/scot/scot209.nsf/veritydisplay/e5a4baa7eed9b492c1256a49004a812e/$file/gsk0400701s0201.pdf

As this is a British standard for all Breakers I would say that no Type B 32amp MCB would "run forever" at 38amps
 
Design basics
Load current equal or less than protective device and cable current carrying capacity equal or greater then protective device so start with load current 9800/230 = 42.6 MCB equal or greater so B45 MCB
Cable 45A or greater see Table 4D5 BS7671 column 6 method C for 10mm cable 64A
Ib 42.6, In 45, It 64 The original B32 MCB is too small repeated overheating may damage the MCB
You did the right thing and changed it
 

Reply to Correct MCB ??? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
780

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top