B

brookster

I have to look at an 11KV/415V transformer with an reported leak due to corrosion - bear in mind I have not seen the transformer but should be at some point tomorrow.
My initial thought on this are if corrosion has set in to this sort of level where leaks are becoming present the best thing to do would be to replace the transformer, any repairs would be temporary at best and would not be advisable in the med-to long term? can anyone tell me if such a repair would be a good course of action it's something I have never seen done.
Also to maintain the site power a generator will need to be installed to be run as a temp measure until works can be completed to replace the 220KVA transformer.
I cannot yet provide any more info on the level of corrosion will update hopefully tomorrow.
 
I have to look at an 11KV/415V transformer with an reported leak due to corrosion - bear in mind I have not seen the transformer but should be at some point tomorrow.
My initial thought on this are if corrosion has set in to this sort of level where leaks are becoming present the best thing to do would be to replace the transformer, any repairs would be temporary at best and would not be advisable in the med-to long term? can anyone tell me if such a repair would be a good course of action it's something I have never seen done.
Also to maintain the site power a generator will need to be installed to be run as a temp measure until works can be completed to replace the 220KVA transformer.
I cannot yet provide any more info on the level of corrosion will update hopefully tomorrow.


Depends where the corrosion and leak is. Best you take a look first and maybe post a photo or two. Yes repairs can and often do get made to transformer casings etc, the type/method of repair being based on the material involved. I've had a brand new 1.6MVA TX tank given weld repairs made on site, after being dropped by a fork lift driver...

At just 220KVA it's a bit of a baby, i guess it depends on just how bad the corrosion and the leak is, whether or not it's past it's useful life or not. The thing is, if oil is leaking out in any quantity, air and moisture could be getting in and contaminating the insulating oil. So maybe worth giving a sample of oil a breakdown test.
 
Last edited by a moderator:
Without seeing it, it’s impossible to say.
Usual suspect points are the radiators and cable boxes. I can recommend a specialist repair company if you want. (Sorry wont mention them in open forum.)
 
An update for those who are interested,

Couldn't get the keys to the cage (AP on hols) but the transformer is in an absolute nic, according to reports today maintenance has not been done on it for over 30 years! I can only imagine what the oil inside is like acidity wise haha! Probably eating it inside out.

IMAG0083.jpg

Leak is actually coming from the bottom of the tank, oil level is probably got 1.5-2 inches before it hits the actual transformer. So very dangerous times indeed.
It needs a new tranny will update more later sorry I couldn't get better pictures but I am more bothered about that than you :D

The whole area is a bunded area so no worries that way chaps, I'm sure you can also see there is NO oil in the sight glass!

I was agitated so I didn't take more pics but right round it spots of rust are everywhere.
 
Wow, she's a small 'un! Is the weep coming from the bottom of the tank adjacent to the radiator? Is it not possible to weld up?. Only seen a repair like this done the once, but a repair was far easier than disturbing the old paper lead cable that was attached to it. Although ensuring the inside was dry, so not a fire risk, whilst preventing the transformer from drying out was another issue...!

The oil, if as old as suggested will probably contain PCB's. Something to consider when mopping up.

Tony will be on later, about 0100-01300 hrs usually. He'll give his expert opion.
 
Last edited:
The leak is actually coming from right under the bottom, agree PCB's are highly probable.
It's not getting repaired its getting replaced.If cables need done they will get replaced too!
You can't really see from that pic but trust me it's not pretty.
 
Despite the rumours PCB’s aren’t that common in transformers. Normally found in power capacitors. Get a specialist in to check, not expensive. Less than £100 as of last week.

Regarding the leak, re-welding tanks is quite common if you get the right company, back flushing the tank would depend on the oil sample results.

Repair or replacement is up to the customer. It’s a baby, but 250KVA are 2[SUP]nd[/SUP] user stock items if you know where to look.

Top the oil up to give you the time to make a reasoned decision. I’ve had to keep a leaking transformer going for nine months before we could take it out of service. 3.3KV bushing leaking around the cable box.

The down side with this one is it doesn’t have conservator to make topping up easy.
 
Despite the rumours PCB’s aren’t that common in transformers. Normally found in power capacitors. Get a specialist in to check, not expensive. Less than £100 as of last week.

Regarding the leak, re-welding tanks is quite common if you get the right company, back flushing the tank would depend on the oil sample results.

Repair or replacement is up to the customer. It’s a baby, but 250KVA are 2[SUP]nd[/SUP] user stock items if you know where to look.

Top the oil up to give you the time to make a reasoned decision. I’ve had to keep a leaking transformer going for nine months before we could take it out of service. 3.3KV bushing leaking around the cable box.

The down side with this one is it doesn’t have conservator to make topping up easy.

The worrying thing is that the oil has not been changed in over 30 years, there is a whole lot of trannys being replaced over the coming years just so happens this one went ---- up.
 
Last edited by a moderator:
The worrying thing is that the oil has not been changed in over 30 years, there is a whole lot of trannys being replaced over the coming years just so happens this one went ---- up.



As the oil is in a sealed environment, it shouldn't ever need changing, not unless there has been some internal fault or moisture has managed to enter and contaminate the oil. Typically every TX should be inspected regularly and oil samples taken to confirm it's insulation properties are within specification with no particles in suspension. How this TX has got to a point where oil levels are so low, it's not registering on the sight glass, means that it has been neglected for a very long time.

Don't be too bothered about rust spots, the tank and cooling pipes are thicker than you may think. Leaks are more likely to be found at bushings and at points of failed poorly made welds...

What do you mean, by this TX going ''---- up'' ??
 
ok, I wouldn't touch that, now there is a company that makes a pot of epoxy stuff (about 50 pounds for 1Kg) that is a temporary patch intended for sort of up to 4 weeks service, it is not permanent and is really only to close off leaks until the thing gets removed.......this transformer looks to me to be from around 1955....don't let the paint fool you, they put lead, cadmium , arsenic and a few other chemicals in there so that it would look like that for 100 years, paint that is banned since about 1990..

This will have PCB's in it (Polychlorinated ByPhenals) which are a nasty long effect damaging poison, and should not be disturbed....what will need to happen is that the Electricity supply company will need to kill it with an axe, then kill it again just to make sure.....and a specialist chemical company will need to have the whole thing away and turf it into a blazing hot metal furnace, the gravel and the concrete around th base will need carting away as well to be chemically washed then disposed of legally.....

This Transformer is (due to the leak) going to cost about 50,000 pounds to get rid of, I don't think the sorbant sheets under it are doing much good...wouldn't touch it as it is a chemical waste issue, and it is a level of contamination that can lead to all sorts of issues, up to jail level...

I have seen a contractor fined 25,000pounds for spilling about 1 litre of oil, and that was after grabbing the phone and calling the environment agency within minutes, and doing everything they could to clean it up....there was a specialist contractor there after that to clean up and they were there for 2 weeks, testing soil and water nearby etc as well.....that had to be paid for too and apparently more than wiped out the whole value of their contract...so be warned...
 
I know of transformers installed in the 30’s sill in use today. They were babies at only 250KVA, no conservators or silica breathers fitted. I can only remember one having the oil filtered.
 
This will have PCB's in it (Polychlorinated ByPhenals) which are a nasty long effect damaging poison, and should not be disturbed....what will need to happen is that the Electricity supply company will need to kill it with an axe, then kill it again just to make sure.....and a specialist chemical company will need to have the whole thing away and turf it into a blazing hot metal furnace

Just what the job needs, a scare monger. How can you say it contains PCB’s without testing.

As for the disposal of PCB’s, steel works wouldn’t touch it. It mainly gets used as a fuel for cement kilns. Higher temperatures and high volatile gas flows with secondary combustion. The kiln also operates under negative pressure so air can only be drawn in and not under the positive pressure of a furnace with a slow moving burden where the gases can be expelled.
 
Last edited by a moderator:
the oldest transformer I remember seeing, was removed about 3 years ago, dated to about 1905, it was still live but the load had been removed/demolished back in the 1970's, the power company had it away when they were in the area re-poling.....

I am going to a place today or tomorrow possibly which has 80 year old power lines going for a distance of about 10 miles, chopped at both ends and just going from a to b with the village they used to power gone since just after the war.....I may take some photos of some of them if I get up there...I actually think they are so old that they are solid copper...the whole lot is bright green....
 
Just what the job needs, a scare monger. How can you say it contains PCB’s without testing.

As for the disposal of PCB’s, steel works wouldn’t touch it. It mainly gets used as a fuel for cement kilns. Higher temperatures and high volatile gas flows with secondary combustion. The kiln also operates under negative pressure so air can only be drawn in and not under the positive pressure of a furnace with a slow moving burden where the gases can be expelled.

Most cement kilns are becoming waste disposal units with a byproduct of clinker nowadays.
 
I'm with Tony here, extremely unlikely that this TX contains PCB's. Relatively very few transformers were insulated with PCB's and i have personally never come across one myself!! For someone that's so jittery being around MV, makes me wonder what your doing in such work place environments?? lol!!


Decently manufactured transformer can have an unlimited lifespan, certainly measured in scores of years, provided it's maintained and it's not worked hard at the top end of it's rating for long periods etc. Most they would need is maybe a nitrogen top-up (depending on it's design) now and again and maybe an oil exchange in it's lifetime.... One of the most reliable electrical components ever made!!
 
I'd agree from my relatively limited experience of MV Tx's they're damn reliable. You cite lack of maintenance as being the underlying issue but I'd also suggest you check for external environmental factors that may be responsible for accelerating corrosion and obviously check all the earthing points are in tact and connected and within impedance recommendations.
 
As the oil is in a sealed environment, it shouldn't ever need changing, not unless there has been some internal fault or moisture has managed to enter and contaminate the oil. Typically every TX should be inspected regularly and oil samples taken to confirm it's insulation properties are within specification with no particles in suspension. How this TX has got to a point where oil levels are so low, it's not registering on the sight glass, means that it has been neglected for a very long time.

Don't be too bothered about rust spots, the tank and cooling pipes are thicker than you may think. Leaks are more likely to be found at bushings and at points of failed poorly made welds...

What do you mean, by this TX going ''---- up'' ??

Acidity checks must be carried out every 3 years to make sure your oil hasn't become highly acidic which would cause problems over time.(Along with other common tests as part of a decent maint programme/ if this had been done the tranny wouldn't be in this condition today.)
A common thing that happens is that the varnish from the windings can increase this acidity level.
To say a transformer shouldn't ever need its oil changing is pretty ???? I know it doesn't quench an arc but it does cool the transformer and protect against corona.

Second point : It's got a hole in it.

As already stated the hole is in the bottom under the tank, once rust has happened on the level on this transformer welding is only delaying the cost of a replacement. It's actually more cost effective to just get a new one, spots are everywhere (bad spots not cosmetic)

Either way regarding PCBs maintenance or testing for PCBs hasn't been done so it's ill advised to just assume they are not present being an unknown.

This WILL have to be tested for to arrange disposal, if none cheap disposal if some dear disposal!
 
Last edited by a moderator:
Most cement kilns are becoming waste disposal units with a byproduct of clinker nowadays.

Thought I’d drag you in with that one!

Solvents, waste printing ink, PCB’s and old tyres all get slung in the kiln mix.

I hope you all believe RoB and I, the emissions and product are contaminate free.

The temperatures are so high nothing survives, if it survives the calcining stage, it won’t survive the pre calciner/pre heat with its secondary fuel injection. The temperatures are stupid. The steel wire in the tyres stood no chance, vaporised and then taken up by the cement kilns raw feed (its so called meal) to improve the cements setting properties.

The emissions are monitored constantly, any reading out of spec and the kiln would automatically revert to just coal as its fuel. Coal has to be there as the ignition fuel for the other crap.

I tested the sampling equipment with known noxious contaminates every day. (I should be dead!)
It was my signature on the emissions log for years!
 
Acidity checks must be carried out every 3 years to make sure your oil hasn't become highly acidic which would cause problems over time.(Along with other common tests as part of a decent maint programme/ if this had been done the tranny wouldn't be in this condition today.)
A common thing that happens is that the varnish from the windings can increase this acidity level.
To say a transformer shouldn't ever need its oil changing is pretty ???? I know it doesn't quench an arc but it does cool the transformer and protect against corona.

Second point : It's got a hole in it.

As already stated the hole is in the bottom under the tank, once rust has happened on the level on this transformer welding is only delaying the cost of a replacement. It's actually more cost effective to just get a new one, spots are everywhere (bad spots not cosmetic)

Either way regarding PCBs maintenance or testing for PCBs hasn't been done so it's ill advised to just assume they are not present being an unknown.

This WILL have to be tested for to arrange disposal, if none cheap disposal if some dear disposal!


Ha-ha, every 3 years?? You been reading this stuff out of a book or manual?? I've never known any TX have it's oil tested every 3 years. The procedure for drawing the oil from the TX can be quite time consuming too, before you can get a sample that is suitable for breakdown testing.

The only time TX oil needs a complete oil change, is if harmful moisture levels has found it's way into the oil and tank etc, or there is or has been internal overheating or fault!! Those are the conditions that would cause any acidity increase from winding varnish too. A typical maintenance based oil test, is to test for the oils KV breakdown value. Any contaminant will reduce the breakdown value, especially suspended carbon particles. Transformer oils these day's are almost all now synthetic, mineral oil is something from the past, that served it's purpose and has now been superseded. Though the probability of mineral oil being used in your TX is pretty much certain...

So what other common tests to the TX are you referring too?? As far as i can see, this transformer has nothing much on it to test!!
 
Ha-ha, every 3 years?? You been reading this stuff out of a book or manual?? I've never known any TX have it's oil tested every 3 years. The procedure for drawing the oil from the TX can be quite time consuming too, before you can get a sample that is suitable for breakdown testing.

The only time TX oil needs a complete oil change, is if harmful moisture levels has found it's way into the oil and tank etc, or there is or has been internal overheating or fault!! Those are the conditions that would cause any acidity increase from winding varnish too. A typical maintenance based oil test, is to test for the oils KV breakdown value. Any contaminant will reduce the breakdown value, especially suspended carbon particles. Transformer oils these day's are almost all now synthetic, mineral oil is something from the past, that served it's purpose and has now been superseded. Though the probability of mineral oil being used in your TX is pretty much certain...

So what other common tests to the TX are you referring too?? As far as i can see, this transformer has nothing much on it to test!!

Yes on HV equipment guidelines are usually followed. Crackle, acidity, breakdown voltage, breathers and corrosion general condition ect.
It's pretty common work with HV maintenance. No one mentioned replacement of oil apart from you....
Oil gets replaced if it fails any of these tests funnily enough.
3 years is also a moderate maint cut off point, we used to do the tests annually.
Drawing oil from a TX time consuming? really?? what half a day to empty and fill it up and 10 mins to draw a sample :D.

Also as must TX are old they will most certainly be filled with OM16 and not midel!
I would go as far as 80% :D
 
Last edited by a moderator:
Yes on HV equipment guidelines are usually followed. Crackle, acidity, breakdown voltage, breathers and corrosion general condition ect.
It's pretty common work with HV maintenance. No one mentioned replacement of oil apart from you....
Oil gets replaced if it fails any of these tests funnily enough.
3 years is also a moderate maint cut off point, we used to do the tests annually.
Drawing oil from a TX time consuming? really?? what half a day to empty and fill it up and 10 mins to draw a sample :DAlso as must TX are old they will most certainly be filled with OM16 and not midel!
I would go as far as 80% :D


I think you'll find Tony mentioned oil filtering, which is basically oil replacement!!

10 minutes to draw a sample?? If that's how long it takes you to get an acceptable sample, then your doing something wrong!! You'll need the flush the sample valve before you even start, that'll be around half a gallon or so of oil gone before you start!! Then you need to clean the sample vessel with sample oil, draw a sample, ...and if bubbles and suspended particles are present, or colour isn't good you need to discard and draw another sample. That could take 2/3/4 samples before an acceptable sample is obtained!! You would ''Never'' i repeat Never, test a sample that's drawn straight off the draw valve. Think you need to check your oil testing procedures again.... The key to any oil sampling is cleanliness. 90% of all oil sample failures, is not adhering to that simple rule!!

If you tested TX oil annually, your TX oil levels would be getting bloody near critical after 10 years. Never heard anything so daft!! Unless the TX has been working hard, near or at it's full KVA rating for long periods, then a full lab oil testing procedure need not be warranted at less than 5 year periods. And to be honest, i know many that have gone for far longer than that.

The other tests you indicated are not tests, but visual inspections, but i'm assuming you are referring to inspection guidelines!!
 
One of the quickest tests for oil is a hot wire test. Heat a steel wire to red heat, plunge it in to the oil, if it foams there is moisture present.
Simple but it will let you know if you have a moisture problem.

I did this on a very old Reyrolle OCB, marked it on the report as oil change required at next inspection. Bloody thing tripped on my watch! Clench bum cheeks, slam the handle forward and run!

Ever tried running while clenching your bum?
 
One of the quickest tests for oil is a hot wire test. Heat a steel wire to red heat, plunge it in to the oil, if it foams there is moisture present.
Simple but it will let you know if you have a moisture problem.

I did this on a very old Reyrolle OCB, marked it on the report as oil change required at next inspection. Bloody thing tripped on my watch! Clench bum cheeks, slam the handle forward and run!

Ever tried running while clenching your bum?

That'll be version of the crackle test, which these day's has fallen by the wayside, as any of the modern KV oil testing meters will give you that crackle if moisture is present, as it's ramping up, or when holding a KV value and the meter stirs the oil.
 
I think you'll find Tony mentioned oil filtering, which is basically oil replacement!!

10 minutes to draw a sample?? If that's how long it takes you to get an acceptable sample, then your doing something wrong!! You'll need the flush the sample valve before you even start, that'll be around half a gallon or so of oil gone before you start!! Then you need to clean the sample vessel with sample oil, draw a sample, ...and if bubbles and suspended particles are present, or colour isn't good you need to discard and draw another sample. That could take 2/3/4 samples before an acceptable sample is obtained!! You would ''Never'' i repeat Never, test a sample that's drawn straight off the draw valve. Think you need to check your oil testing procedures again.... The key to any oil sampling is cleanliness. 90% of all oil sample failures, is not adhering to that simple rule!!

If you tested TX oil annually, your TX oil levels would be getting bloody near critical after 10 years. Never heard anything so daft!! Unless the TX has been working hard, near or at it's full KVA rating for long periods, then a full lab oil testing procedure need not be warranted at less than 5 year periods. And to be honest, i know many that have gone for far longer than that.

The other tests you indicated are not tests, but visual inspections, but i'm assuming you are referring to inspection guidelines!!

and were did you get my test procedures from :D, stop making ****e up.

Top the thing up :D

Yes 10 minutes to draw a sample, bubbles go away on there own and yes never take first draw :D

Stop trying to catch me out mate you won't. The daftest thing I've heard is that trannys don't need maint!

Any site worth it's salt that looks after it's equipment to a high standard will have a three year maint program on trannys it's pretty much bog standard anywhere I've worked granted it's all MOD sites but most large sites or companies employ such high standards.

Your attitude i.e 'it will be fine' is the reason things go bang in the night.

'or colour isn't good you need to discard and draw another sample' this statement I can confirm as absolute pash, the colour of oil is the same throughout. Also the colour of the oil means absolutely nothing in regards to passing or failing ANY test. LOL

Just stick to drilling live bus bars :D
 
Last edited by a moderator:
Tranny’s are high maintenance. The make up costs a bloody fortune!

You’re company can set whatever testing period it likes. It doesn’t make it a national standard, it’s you’re company standard!
I’ve worked on 100’s of power transformers. Only ever changed the oil in three of them. all of the three had tap changer problems so tripped on Buchholz gas.
 
and were did you get my test procedures from :D, stop making ****e up.

Top the thing up :D

Yes 10 minutes to draw a sample, bubbles go away on there own and yes never take first draw :D ha, ha, ha!! I suppose the fact that their shouldn't be any bubbles is quite irrelevent to you then??


Stop trying to catch me out mate you won't. The daftest thing I've heard is that trannys don't need maint! I'm not trying to catch you out at all, your doing a pretty good job of that yourself!! I didn't say that, i saying, that most trasnsformers don't get much in the way of actual maintenance, most are lucky to get a regular visual inspection... And for better or for worse, that's the truth of the matter!!

Any site worth it's salt that looks after it's equipment to a high standard will have a three year maint program on trannys it's pretty much bog standard anywhere I've worked granted it's all MOD sites but most large sites or companies employ such high standards. MOD eh, that makes some sense then, they aren't spending their own money!!

Your attitude i.e 'it will be fine' is the reason things go bang in the night. Never had a TX go bang yet, and i wouldn't mind betting, i've fully tested more MV/LV systems (including the TX's) than you've come close too, over the years!!

'or colour isn't good you need to discard and draw another sample' this statement I can confirm as absolute pash, the colour of oil is the same throughout. Also the colour of the oil means absolutely nothing in regards to passing or failing ANY test. LOL ....Again you seem not to have a clue as to what oil colour changes can and do indicate as to what's going on in the Transformer!!

Just stick to drilling live bus bars :D
I suggest you leave TX maintenance to those that actually know what they are doing, and what they should be looking for!! ....It's certainly not your forte!!

You have proved to me you know very little, probably only what you've been told by others, and you haven't quite got that right either!! Oh, and unlike you i don't have to make anything up, least of all the crap your trying spurt out.

The colour of the oil at the very bottom of the tank (where the draw valve is located) can be quite different to that oil which is circulating. It's where all the crap falls too!! It's you, that's coming out with all the ''pash'' mate!!
 
Last edited by a moderator:
That'll be version of the crackle test, which these day's has fallen by the wayside, as any of the modern KV oil testing meters will give you that crackle if moisture is present, as it's ramping up, or when holding a KV value and the meter stirs the oil.

It’s rough and ready I know. But a quick test it will show moisture. When doing a PILC cable I’d dip a sample of the papers in the hot compound, again if it foamed we had a problem.

I went to GEC to see some OCB’s they were doing up for me.
They then came and did the oil tests on site after I refused to accept them back. The oil had carbon deposits. The carbon had dislodged from the top of the tank in transport. The oil passed but they agreed it didn’t look good so changed it as a good will gesture.
Interesting to see the test rig in action.
 
You have proved to me you know very little, probably only what you've been told by others, and you haven't quite got that right either!! Oh, and unlike you i don't have to make anything up, least of all the crap your trying spurt out.

Wrong on so many level smart arse!

The colour of the oil at the very bottom of the tank (where the draw valve is located) can be quite different to that oil which is circulating. It's where all the crap falls too!! It's you, that's coming out with all the ''pash'' mate!!

No its not - it really isnt :D - crap falling to the bottom - do you want a darwin award it's called gravity.

and were did you get my test procedures from :D, stop making ****e up.

Top the thing up :D

Yes 10 minutes to draw a sample, bubbles go away on there own and yes never take first draw :Dha, ha, ha!! I suppose the fact that their shouldn't be any bubbles is quite irrelevent to you then??

You do know that the bubbles are made as you draw the bloody oil out the valve!!!

Stop trying to catch me out mate you won't. The daftest thing I've heard is that trannys don't need maint!
I'm not trying to catch you out at all, your doing a pretty good job of that yourself!! I didn't say that, i saying, that most trasnsformers don't get much in the way of actual maintenance, most are lucky to get a regular visual inspection... And for better or for worse, that's the truth of the matter!!

Thats absolute crap LOL

Any site worth it's salt that looks after it's equipment to a high standard will have a three year maint program on trannys it's pretty much bog standard anywhere I've worked granted it's all MOD sites but most large sites or companies employ such high standards. MOD eh, that makes some sense then, they aren't spending their own money!!

And you would know that how exactly?

Your attitude i.e 'it will be fine' is the reason things go bang in the night. Never had a TX go bang yet, and i wouldn't mind betting, i've fully tested more MV/LV systems (including the TX's) than you've come close too, over the years!!

I can guarantee you've not, considering you look at them every ten years or so if at all. Some poor so has probably been left with your crap of an install to fix after some douche forgot it need looked at every so often.

'or colour isn't good you need to discard and draw another sample' this statement I can confirm as absolute pash, the colour of oil is the same throughout. Also the colour of the oil means absolutely nothing in regards to passing or failing ANY test. LOL ....Again you seem not to have a clue as to what oil colour changes can and do indicate as to what's going on in the Transformer!!

I've seen more oil than the rigs in Saudi Arabia - it means fck all otherwise it would be pretty important in TX maint - I hate to break this to ya - it's not - PERIOD.
It can give an INDICATION which other tests will shed some light on!!!
Finding other things (IE carbon or Iron deposits) is not the colour either so stop backtracking/twisting , keep digging.)
You find me a guy who can tell me whats wrong with a TX by the colour of the oil and i will find you a liar.


Just stick to drilling live bus bars :D
I suggest you leave TX maintenance to those that actually know what they are doing, and what they should be looking for!! ....It's certainly not your forte!!

And that my son I can guarantee is not you :D

You said some of the things you have said on this forum working for any reputable HV company your arse wouldn't even hit the door.

Guru tell me how I would go about finding where the hotspots on my core would be or what I would use to find them and how I would use it?

And why would this be a problem and how could I go about changing this problem :D

No google now

I'll say it again - I don't take advice from people who drill live bus bars :D not really good practice or is that how it's done also? Must have missed that one too :D

Keep your limited knowledge and bad practice in China, k thanx.
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Corrosion Transformer
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
28

Thread Tags

Tags Tags
transformer

Advert

Thread statistics

Created
brookster,
Last reply from
Marvo,
Replies
28
Views
4,847

Advert

Back
Top