Being relatively new to EICR testing, I was not totally sure how best to enter a couple things found on an old house periodic earlier this week, and would be grateful for opinions.
1. For a single 13A socket that had been connected as a spur at the fuse board (with 2.5mm2 cable) to the wrong side of a fuse - so it's only protection is the DNO fuse - what would you put on the test sheet for the protective device? The DNO fuse type/rating etc, or a statement that is has no protection (since the DNO fuse is covered separately)?
2. For the same fuse board, if fuses 1 and 2 are for the N of two socket circuits, and fuses 3 and 4 are for the L of the two socket circuits, again how best to enter on the test results schedule? A note against positions 1 and 2 that these are fused neutrals, and the actual circuit data and test results against positions 3 and 4?
And record as C2 in both cases?
Steve.
1. For a single 13A socket that had been connected as a spur at the fuse board (with 2.5mm2 cable) to the wrong side of a fuse - so it's only protection is the DNO fuse - what would you put on the test sheet for the protective device? The DNO fuse type/rating etc, or a statement that is has no protection (since the DNO fuse is covered separately)?
2. For the same fuse board, if fuses 1 and 2 are for the N of two socket circuits, and fuses 3 and 4 are for the L of the two socket circuits, again how best to enter on the test results schedule? A note against positions 1 and 2 that these are fused neutrals, and the actual circuit data and test results against positions 3 and 4?
And record as C2 in both cases?
Steve.