Just got back from looking at a potential job. What a bodge up!

I was called around to be asked to install an isolator for a sub main feeding a consumer unit which a car charger company will come off feeding their charger.

New mains upgrade recently done and the previous electrician has bodged a bit of 16mm t and e straight into a henly block from the meter to feed secondary consumer unit.

I’m thinking the cpc within the 16mm may be undersized but just wanted to clarify if my calculation is correct (it’s been a while)...

The size of fuse I’m thinking of installing is a 50A type b (either RCBO or mcb with rcd main switch).

S = 250A x 11 (squared) / 115 = 7.2mm??

CPC is 6mm.

The sub main in question has no bonding attached to it and is approximately 15mtrs away from main board running underneath the floor.

Please correct me if I’m wrong, it’s been a while!

thanks
 
I don’t need to know the load at the consumer unit end, I just want to make the sub main safe which is why I’m going to add a fuse making sure it’s the biggest / safest one.

My thoughts were to add a 63a double pole RCD controlling a 50A MCB, the part I’m stuck on is the CPC calculation,

You say you want to fit the best fuse for the job, then say you are going to fit an MCB, this makes no sense? An MCB is not a fuse, and a fuse is better than an MCB for protecting distribution circuits.

If you don't know the load at the consumer unit how can you know whether the ocpd you install is correct?
 

Reply to CPC calculation in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
277
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
672
  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top