Just got back from looking at a potential job. What a bodge up!
I was called around to be asked to install an isolator for a sub main feeding a consumer unit which a car charger company will come off feeding their charger.
New mains upgrade recently done and the previous electrician has bodged a bit of 16mm t and e straight into a henly block from the meter to feed secondary consumer unit.
I’m thinking the cpc within the 16mm may be undersized but just wanted to clarify if my calculation is correct (it’s been a while)...
The size of fuse I’m thinking of installing is a 50A type b (either RCBO or mcb with rcd main switch).
S = 250A x 11 (squared) / 115 = 7.2mm??
CPC is 6mm.
The sub main in question has no bonding attached to it and is approximately 15mtrs away from main board running underneath the floor.
Please correct me if I’m wrong, it’s been a while!
thanks