Hi guys, i just changed a 8.5kw electrical shower for a friend, the live is 6mm2 and i believe it is fine, the only thing is the cpc, looks like 1.0mm, at most 1.5mm, i checked codes, but still not sure about it, is this cpc ok?

cheers
 
Hi guys, i just changed a 8.5kw electrical shower for a friend, the live is 6mm2 and i believe it is fine, the only thing is the cpc, looks like 1.0mm, at most 1.5mm, i checked codes, but still not sure about it, is this cpc ok?

cheers

First response to a post for me. Assuming both protective and line conductors are copper, then according to table 54.7 in regs (pg 130 in mine), suggests csa of protective conductor should be (at least) same as line conductor?

Thats the way I'm reading it anyway, but have to admit I've never seen a 6mm cable with a 6mm earth? Having said that, if you can imagine nearly 40amps running down your skimpy cpc in a fault condition then it doesn't sound ideal to me!

Pat
 
Last edited by a moderator:
First response to a post for me. Assuming both protective and line conductors are copper, then according to table 54.7 in regs (pg 130 in mine), suggests csa of protective conductor should be (at least) same as line conductor?

Use the adiabatic equation.
 
Hi,
Whats the length of the cable and how is it run ( under floorboards, clipped direct etc ).

You said its old cable, is it the old colours Red, Black ??

You also mentioned 8.5kw shower, so that equates to 36.95 amps ( ib ), so depending on your fuseboard, you need at least a 40amp mcb.

So work out your current -carrying capacities, volt drop and adiabatic to get correct cable selection. You should really know what size cable you have selected, as this can have a big effect when the shower is on ( over heating the cable etc ).

Hope this helps,
Sav
 
Hi,
Whats the length of the cable and how is it run ( under floorboards, clipped direct etc ).

You said its old cable, is it the old colours Red, Black ??

You also mentioned 8.5kw shower, so that equates to 36.95 amps ( ib ), so depending on your fuseboard, you need at least a 40amp mcb.

So work out your current -carrying capacities, volt drop and adiabatic to get correct cable selection. You should really know what size cable you have selected, as this can have a big effect when the shower is on ( over heating the cable etc ).

Hope this helps,
Sav

i only changed the shower and did not touch anything else. the colors are old: read and black. 6mm.

i could find easily the minimum size of main bonding conductor is 10mm, but just cannot find minimum requirement for cpc in the bs7671, is 1.5mm really ok?
 
i have not done the adiabatic equation, but guessing as some of the results i got previously from using that equation, they maybe , yes .

BUT, you must make sure you do it properly i.e supply protective device etc.....

Sav
 

Reply to CPC for shower! in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
687
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

I’m sure I’ve seen an LSF round cable used on sites before as well with an insulated earth. Not flex, something a bit more substantial but not FP...
2
Replies
21
Views
4K
  • Question
I went to look at a job like this a few years ago. My customer had a rental house, where there was an upstairs bedroom that had a newly built stud...
    • Informative
    • Like
2
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top