Ive just changed a Consumer board and fitted a Wylex split load,5 Rcbo's one side and 4 Mcb's on the Rcd side. After connection of all conductors (all in correct terminals) it turns out one leg of my ring has a faulty Cpc, i've carried out an IR test and there's an issue with the neutrals & one Cpc, however ive disconnected every outlet in the house and all terminals are present and tight, I'm assured there are no hidden JB's etc so i am baffled. Could anyone possibly nudge me in the right direction??

Thanks
 
Right, I've only read the first five replies and am quite frankly astonished that this hasn't come up at this point. Not wanting to risk reading any more drivel, I apologise if I'm repeating what has already been said.

1. Why are you only finding out about this fault once you've fitted the board? Why are you energising a circuit that you do not know is safe? As far as I'm aware, even the five week wonder courses are teaching to do earth cont and megger tests before juicing up. Firing up a circuit you haven't tested is completely irresponsible and is just asking for trouble.

2. How have you not considered the possibility of damage to the cable between outlets, i.e. someone putting a nail or screw through one when putting up a picture?

Good God I realise this forum has had a brain drain since I was last about but seriously? How has this even got to 5 replies without someone spotting these fundemental problems? Sorry to be a douche, but this has properly wound me up.
 

Reply to CPC - Neutral Fault in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
325
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
852
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
973

Similar threads

  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top