Hi guys, just a quick one.

If you have a TNCS system, then the main earth is 16mm

Instead of going to a CU it goes to a 60A switch fuse. from the switch fuse to the consumer you would use 16mm cable.
My question is would you still need to have a 16mm earth going through the switch fuse to the CU.
It would seem to me that you could go from the MET in 16mm and then it could be reduced to the CPC with the 16mm cable.

Thanks in advance
 
Coming out of the load side of your switchfuse you have your distribution circuit which you cansize accordingly using appropriate calcs CCC, VD, thermal constraints, shock protection etc etc.

The TN-C-S 'rules' will only apply to the supply tails & main earthing conductor supplying your switchfuse.

The only additional consideration in this instance is your protective bonding conductors and where they will be connected.
 

Reply to the thread, titled "CPC size from switch fuse" which is posted in Australia on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
CPC size from switch fuse
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
2
Unsolved
--

Advert

Thread statistics

Created
gooner85,
Last reply from
i=p/u,
Replies
2
Views
1,191

Advert

Back
Top