m1ck_b87

Hi guys.

Correct me if I'm wrong your cpc and earthing conductor should be no less than half the size of your line conductor.
 
Wrong. See section 543 of BGB
 
Cpcs and the earthing conductor are sized by the adiabatic equation or can be selected (comparing to the associated line conductor csa and giving a higher csa) from table 54.7.
Bonding conductor csas are selected from table 54.8 according to the size of the supply neutral conductor.
 
Cpcs and the earthing conductor are sized by the adiabatic equation or can be selected (comparing to the associated line conductor csa and giving a higher csa) from table 54.7.
Bonding conductor csas are selected from table 54.8 according to the size of the supply neutral conductor.

Only on PME earthing supplies!!
 
Cpcs and the earthing conductor are sized by the adiabatic equation or can be selected (comparing to the associated line conductor csa and giving a higher csa) from table 54.7.
Bonding conductor csas are selected from table 54.8 according to the size of the supply neutral conductor.

Dear Mr. Richard

I don't want to be picky, I just want to clarify this for myself, but isn't that better if instead of LINE we use LIVE or NEUTRAL on that statement?

Regards
R&M
 
Technically 'Neutral' is a 'Live' conductor. So Mr.Richard would be correct.

Dear Mr. Sparky

That's exactly my point. LIVE or NEUTRAL are correct. But if you notice in the statement it says LINE. I believe that is not correct. I will be appreciate for correcting me if I am wrong.

Regards
R&M
 
Both Live and Neutral are LINE conductors and will be the same size therefore the cpc for the cable (or the earth conductor for the applience) will be in ratio to the LINE conductor regardless if it is Live or Neutral.
 
Both Live and Neutral are LINE conductors and will be the same size therefore the cpc for the cable (or the earth conductor for the applience) will be in ratio to the LINE conductor regardless if it is Live or Neutral.

With respect but I believe you are wrong on this.

Both LINE and Neutral are LIVE .

Regards
R&M
 

Reply to cpc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
273
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
267
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

It’s difficult to advise on an electrical issue when some isn’t very conversant with electrical terminology.
Replies
14
Views
1K
totally agree
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top