Chris86
-
Hello All,
After a bit of help regards ZS testing on a Crabtree Starbreaker board.
Have replaced 2 lengths of dado trunking in our office block at work and the measured ZS is coming out much higher than the calculated value.
Section 1 - calculated 0.5 ohms, measured 1.92 ohms.
Section 2 - calculated 0.42 ohms, measured 1.68 ohms.
I am convinced it's the RCD causing the higher readings so wanted to check ZS on incoming and outgoing terminals and compare the 2 but as it's Starbreaker with the internal busbar, there are no line terminals to test on. Is there any way I can test this or will I just have to rely on the calculated readings?
I have checked circuits supplied from the non RCD side of the board and the measured and calculated values are equal.
Sorry if it's a daft question but I haven't done a great deal of testing on domestic boards (we are factory based and all our stuff is Schneider or Red Spot 3 phase) and this is the first Crabtree board I have come across.
Thanks and ATB
Chris
After a bit of help regards ZS testing on a Crabtree Starbreaker board.
Have replaced 2 lengths of dado trunking in our office block at work and the measured ZS is coming out much higher than the calculated value.
Section 1 - calculated 0.5 ohms, measured 1.92 ohms.
Section 2 - calculated 0.42 ohms, measured 1.68 ohms.
I am convinced it's the RCD causing the higher readings so wanted to check ZS on incoming and outgoing terminals and compare the 2 but as it's Starbreaker with the internal busbar, there are no line terminals to test on. Is there any way I can test this or will I just have to rely on the calculated readings?
I have checked circuits supplied from the non RCD side of the board and the measured and calculated values are equal.
Sorry if it's a daft question but I haven't done a great deal of testing on domestic boards (we are factory based and all our stuff is Schneider or Red Spot 3 phase) and this is the first Crabtree board I have come across.
Thanks and ATB
Chris