Hello All,

After a bit of help regards ZS testing on a Crabtree Starbreaker board.

Have replaced 2 lengths of dado trunking in our office block at work and the measured ZS is coming out much higher than the calculated value.

Section 1 - calculated 0.5 ohms, measured 1.92 ohms.

Section 2 - calculated 0.42 ohms, measured 1.68 ohms.

I am convinced it's the RCD causing the higher readings so wanted to check ZS on incoming and outgoing terminals and compare the 2 but as it's Starbreaker with the internal busbar, there are no line terminals to test on. Is there any way I can test this or will I just have to rely on the calculated readings?

I have checked circuits supplied from the non RCD side of the board and the measured and calculated values are equal.

Sorry if it's a daft question but I haven't done a great deal of testing on domestic boards (we are factory based and all our stuff is Schneider or Red Spot 3 phase) and this is the first Crabtree board I have come across.

Thanks and ATB

Chris
 
I know this is a really old thread, but to correct something for future searches, the Di-Log can in fact do a high current test, is it just stupidly obscure. Basically setting the tester to L-N makes it do a high current test. Join N and Earth together, either use both probes on earth conductor under test or join the leads together.
Di-Log themselves published this:

[ElectriciansForums.net] Crabtree RCCB and ZS testing
 

Reply to Crabtree RCCB and ZS testing in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
814
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
873

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
696
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
949

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top