i have had the same fault 3 times recently checked every thing and scratched my head new RCD and not been back since
 
We have recently come across a similar problem, with no answers yet. We replaced a 100ma rcd, up front on a TT system which was tripping out weekly.
Replaced it with 30ma which started tripping out imediately and irritatingly, ittermittantly and without consistancy. Would not trip at x1 & x5, so like you guys, thought faulty rcd.
Went back later with new rcd and having checked my meter. New rcd, very same problem.
Ok, if there is an earth leakage fault, yes the rcd will trip but surely when you test it it would trip? These are just not tripping under test conditions! can anyone explain? Please.
We put the 100ma back on for now.
 
You say your on a tt system are you near to the sub-station by any chance this may cause you issues also believe it or not street lights etc have been known to cause tripping but they are easier to work out due to the lights timings
 
Thanks Darkwood, one of my spark colleagues found some info on interference from sub-stations nearby, which suggests that the harmonics cause a dc component in the supply which as we know from the de-loc principle stops the rcd tripping. And causes nuisance tripping! Does any one know more about this possible cause and its remedy?
 
Thanks sparkswillfly, if this were the case would the rcd not test normally? Instead we've had two rcd's that will not trip at x1 or x5 and one even tripped with all mcb's on the off position, no loads and no test equipment.?
 
Do a ramp test with all normal loads running then do a full rcd test with all loads disconnected this will give you the difference which is the leakage present under normal conditions been a tt system clamping the earth on the rod might not give you all the leakage as it may choose other routes as well, also to be noted is neighbouring premises with leakage can in some situations create nuisance tripping too when this starts been the case or similar unresolved reasons then the expensive option of main switch and full board or rcbos instead this gives easier diagnostics if fault is present, and consider several visits will start to cost alot it can sometimes be just as easy to do this for similar cost.
 

Reply to Crabtree starbreaker rcd fault in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
500
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
693

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top