martinh287

Hi guys got to test a job tomorrow which I know has been installed incorrectly before I have even gone to the job but our "senior electrician" has done the work and my boss wont do anything about him.

Anyway 200a selective vels unit with 35 mm 4 core swa feeding a 3 phase disrubution board 140m away My colleagues have install 25mm double insulated tails to a single phase 100a selective vels unit ( single phase taking from black phase / no balancing out of the phases to accomadate for this ) the 100a vels unit is approximately 3m away and inturn feeds 70 16mm2 3 core swa to another disrubution board with a couple of circuits on.

I am ment to complete a eic and return to my boss to sign off the work.( I wont sign off the work for the company as the work is never to my standard) I will just test the circuits record results and note deviations.

There are the obvious problems.undersized cables for the overcurrent device ( which my boss will argue rcd covers it).balancing out of the black phase. problem is I know when running parrellel circuits off the same breaker has to be done with equal length s of the same size csa but I want to be clear on the reasoning for this before I jump in with both feet
 
Last edited by a moderator:
Been today and installed 50mm2 double insulated tails from the 200a to feed 2 x 100a src units for the 2 circuits. Still has two completly different circuits coming away from the srcs one been the 140m 35mm2 with a load of 54a the second circuit been 70m 16mm2 4 core swa with a load of only 15a. I believe this still to be incorrect with regards the parrellel paths coming away from the 200a but I am still unsure of tge technical reasons for this.

If someone cound help explain would be appreciated. Thanks in advance
 
Been today and installed 50mm2 double insulated tails from the 200a to feed 2 x 100a src units for the 2 circuits. Still has two completly different circuits coming away from the srcs one been the 140m 35mm2 with a load of 54a the second circuit been 70m 16mm2 4 core swa with a load of only 15a. I believe this still to be incorrect with regards the parrellel paths coming away from the 200a but I am still unsure of tge technical reasons for this.

If someone cound help explain would be appreciated. Thanks in advance



I would, if i could understand your terminology!! So i'll leave it to others that maybe can understand it!! ... lol!!
 
Srcs meaning selective residual current units. Basically its a 60898 mcb with 26946 shunt attached and the tails are fed thou a vels unit to detect the imbalances.
 

Reply to crazy in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
614
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
522

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top