I think I've sussed this, but I just wanted to check that I'm doing this correctly according to the latest regs.
I have a customer that wants his garage come workshop on its own circuit as it has lots of high power tools such as lathes etc. Currently it is on a ring final that is shared to a Utility room and a home cinema - Not the best of ideas really.
So I've traced the ring so I know where it starts and finishes, so my thought was this.
Disconnect the ring at the the last socket where it leaves the workshop. Add a 20A MCB into the DB and connect this to the workshop sockets, and done, one radial circuit for the workshop.
Now, I can either put in a new cable from the end socket on the ring which I've just disconnected back to the DB, thus recreating the ring, or put in a maintenance free 32A junction box and extend the cable back to the DB.
What would be the better option ? The DB is in the workshop, and the Utility room is next door, so everything is very close together (within 3 or so metres).
I have a customer that wants his garage come workshop on its own circuit as it has lots of high power tools such as lathes etc. Currently it is on a ring final that is shared to a Utility room and a home cinema - Not the best of ideas really.
So I've traced the ring so I know where it starts and finishes, so my thought was this.
Disconnect the ring at the the last socket where it leaves the workshop. Add a 20A MCB into the DB and connect this to the workshop sockets, and done, one radial circuit for the workshop.
Now, I can either put in a new cable from the end socket on the ring which I've just disconnected back to the DB, thus recreating the ring, or put in a maintenance free 32A junction box and extend the cable back to the DB.
What would be the better option ? The DB is in the workshop, and the Utility room is next door, so everything is very close together (within 3 or so metres).