W
workbelt12
Hi - how does everyone get on crimping these compacted conductors. they are way smaller diameter than standard
equivalent size. Icould get a 25mmlugonto a 35mm conductor. whats best practise?
Do you mean tri-rated ?... never heard the term compacted conductors - copper used in electrics is as compact as it gets, you cannot make it smaller, if you mean the various arrangements of the core 'solid, strandard and tri-rated' as well as shaped conductors in larger SWA's that benefit the cable by reducing its O/D as well as saving on material.
Please be more specific, your slang is not recognised industry terminology.
Could you please cascade the information you have amassed down the chain, we can the apply some lateral thinking to your question, failing that we could hold a conference and determine our thoughts.
A compacted conductor has a reduced o/d for same csa. Therefore a cable lug is very loosei prior to crimping, when using a hex die crimper are lugs on tight enough ?
These cables are vey common, the larger the size the more apparent the difference.
there is no such thing as a compacted conductor, post a link to the cable.
it will be tri-rated
We still don't know whether you mean coarse stranded shaped conductors or fine stranded tri rated conductors, or something else.
The only advice I can give you is to follow the regs, good practice, and your training to provide a mechanically and electrically sound joint suitable for the purpose it is to be used for.
It sounds like you mean shaped conductors 'a common term' like you get in SWA... more an overall triangle shape as oppose to a circular, regardless of the shape etc they still have the same csa but the triangle arrangment usually takes more lug space ironically than a circular formation and can requires to be adjusted to a more circular arrangement to get them in the lug.
I'm, like others are still confused to your use of the word compacted...
PS ...seen your link now ...I call these shaped conductors and you should be able to get the correct lug for them from the same supplier you got the cable, the hole will be smaller but the lug outer diameter will still fit the correct crimp dye.
Swapping lugs till they seem to fit may give a poor crimp without you realising and the lug would also indicate the cable was sized smaller csa than it actually is.
Klauke Textron: blue connection - the solution for compacted conductors
http://www.klauke.com/blue-connection/assets/files/Klauke-blue-connection-en.pdf
Page 7 shows compacted conductors.