Hi - how does everyone get on crimping these compacted conductors. they are way smaller diameter than standard
equivalent size. Icould get a 25mmlugonto a 35mm conductor. whats best practise?
 
The PDF that Archy links to above (from a manufacturer selling lugs specifically for these "compacted conductors") says (p6):

Modern compacted conductors are much thinner than their comparable predecessors. So nowadays, cable manufacturers can often save on sheathing and insulation. This difference is not always obvious at first glance. But it does mean that tubular cable lugs and connectors that look as if they fit have too much play and can no longer be crimped as required. In the past, you have only been able to reliably avert this safety risk using additional sleeves on compacted conductors.


Perhaps the last sentence answers the original poster's question - use sleeves.
 
Agreed - don't use undersize lugs. The tube is designed to deform by a certain amount during crimping and an excess cross-section of copper will prevent this, leading to a weak crimp. In theory the crimping compacts the conductor completely no matter how it starts out, so a lug of the correct CSA may work on a compacted conductor so long it remains properly centralised, but that is uncertain. Hence, the cable-specific crimps are best.
 
The way I've been taught is that if you have a compacted/shaped conductor, use the right lug and crimp. The contact should be OK as Lucien said. If need be, then swap one die for the next size down and re-crimp. For triangular Al cables, DON'T just jam them in whatever round lug fits, they need a matching lug that is then indent crimped.
 
The way I've been taught is that if you have a compacted/shaped conductor, use the right lug and crimp. The contact should be OK as Lucien said. If need be, then swap one die for the next size down and re-crimp. For triangular Al cables, DON'T just jam them in whatever round lug fits, they need a matching lug that is then indent crimped.

I wouldn't ever consider doing this, you risk deforming the lug and ending up with a poor joint.
 
I was hoping for educated replies. If you Google 'Compacted Conductors' before making uninformed
replies you could possibly learn about issue. Then post meaningful & helpful replies

This is an Electricians Forum and you posted a question more suited to Electrical Engineering, the use of these cables is outside the scope of most members on here and those that may have come across them would use the term Shaped conductors, now looking into it it seems this is more common for the big heavy cabling associated with large LV supplies or HV where saving on materials can mean many thousands if using a lot of it.
You have chosen a question that overlaps two bounderies of electrical work thus the original confusion, if I post any number of questions both an Electricians Forum and an Engineering Forum I would in some cases expect 2 contradicting answers due to the nature of differing terminologies and practices.

Yes your question was a good one and you provided a link which I asked for, but I was writing my post as your posted a link before I requested it...just forum timing and order of posts.

Please don't take the confusion and replies as uninformed babble it was just one of those questions that caught us off guard, even me who is industrial, I still know these cables as shaped conductors and was taught that way, if other sectors call them different then fair do.
 

Reply to Crimping compacted conductors in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
356
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
909
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
My older card has it but my newer card doesn’t
    • Like
Replies
1
Views
746
  • Question
Gents has anyone done an application using the UKPN smart connect portal for a split phase supply and addition of multiple single phase battery...
Replies
0
Views
401

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top