R<50v/Ia

How do you arrive at the 0.05 figure as Ia being the operating current in amps (like scots spark said would generally be 100 Amps so 50/100 =0.5
I have the regs and GN3 so I know the figure is 0.05
So how does one arrive at the figure?
Cheers Scott
 
Is it that the 0.05 is what you are hoping to get below if you were to measure the resistance between two pipes, say hot and cold water pipes for example. If its above this then you would have to bond them together. think thats what GN3 is saying on p 35.

This equation, are you supposed to use the cut out or your RCD rating?
If you have a 60A cut out does this mean its got to be below 0.8? (50/60)
and if you do the equation with a 30ma RCD it comes out at 1667 !

To be honest really struggling to get my head around all this !!
 
Gravid the 1667 figure look familiar???? it should its the max ZS for 30ma rcds up to 230v (see page 50brb.)
the resistance measured is between the pipe and the MET at the D.B subtracting the long lead and test leads.

Use the RCD tripping currrent when using the formula. As you have the resistance and the In of the protective devics if you transpose your formula to rxIn <50 then you are ok as any voltage present in the metalwork during fault conditions is less than 50v (touch voltage) remember 120v dc


0.05 is normally used it goes on the side of safety as with the tripping times. If you are above 0.05 then either do the maths and prove if it need bonding ok put in supplimental bonding so its under 0.05. ()for all the time it takes i would bond it)
 
Last edited:
Yes mate i've got it now, just had to go back to the basics, i understand your making sure the touch voltage in the event of a fault doesn't go above 50v.
 

Reply to Cross Bonding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
501
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
974
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

If you can see a piece of plastic entering from the ground then (as cliff said), it does not need main bonding. I think (not sure) this is reg...
Replies
3
Views
442
  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top