I'm not going to touch it but I've a PV system installed that has CT clamp in supply meter. What does this do, why does it increase my import from grid?
 
In itself, it's not capable of increasing your import from the grid. If you're moving it and the reading is changing, that's to be expected (to an extent) because whilst CTs are pretty good, they are not as accurate as direct measurement.

What it does is convert a fluctuating magnetic field into a voltage that represents the current flowing in the cable it is clamped around.

It works because the magnetic field strength is proportional to the current flowing in the conductor and the voltage from the CT (which is essentially a coil of wire) is proportional to the field strength. So, higher voltage = higher current. Moving it will alter the field strength and thus it may appear to increase or decrease the current it is reading. The reality is it's not changing it, it's just exagerating the inaccuracy inherent in this measurement method.
 
In itself, it's not capable of increasing your import from the grid. If you're moving it and the reading is changing, that's to be expected (to an extent) because whilst CTs are pretty good, they are not as accurate as direct measurement.

What it does is convert a fluctuating magnetic field into a voltage that represents the current flowing in the cable it is clamped around.

It works because the magnetic field strength is proportional to the current flowing in the conductor and the voltage from the CT (which is essentially a coil of wire) is proportional to the field strength. So, higher voltage = higher current. Moving it will alter the field strength and thus it may appear to increase or decrease the current it is reading. The reality is it's not changing it, it's just exagerating the inaccuracy inherent in this measurement method.
Thanks. I'm not an electrician and have no intention of doing anything with it. The generation meter installed with my PV system shows more being imported than consumed within the home. The installers say it is because of the CT clamp. It is only about 0.5 kwh a day but it all costs!
 

Reply to CT clamp use in PV system in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
904
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I seem to recall that written information for their approved installers listed an explicit requirement that it be wired and connected in all...
2
Replies
16
Views
1K
Hi My first post here, so apologies for any mistakes. I think it will be DIY job with electrician sign off if required, but would like to do as...
Replies
0
Views
193

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top