- Joined
- Feb 20, 2011
- Messages
- 969
- Reaction score
- 430
You didn't mention the I boost, lets get one inverter working first!
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss ct clamps too close together? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
If each inverter has it's own individual AC isolator just turn two off, removing CTs will not do anything helpful.
Has this system ever worked for any extended period of time without faulting ?
Hi - Some invertor manufacturers advise using 100mA RCD on them. If you've the details we might be able to check. Also please confirm if you mean 30mA where you've said 30ms in #24 .
Changing the consumer unit RCD from 30mA to 100mA may not be possible here as the 30mA RCD may still be required for the other circuits.
Hi - thanks - do you know the installation earthing type and any test results?
Ok, what is attached to the RCD that trips?
Reply to ct clamps too close together? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net