M
mcl
Hi
Am pricing for CU change for a single barn holiday cottage. Forms part of a group. All the meters are in one building at the end, approx 30m away from the CU at this barn. Seems like all ducted underground. The main fuse is 60a, and the Meter tails are 16mm so ok but the main earth (supply PME) is only 10mm2. I think it would be very difficult and costly to get 16mm upgraded main earth back to Western Power fuse.
Thought that another option is forget the PME main earth and TT locally (just other side wall with CU) to the CU?
What do you think?
Thanks MATT
I'd leave the 10mm in. Just note it on your cert.
Thanks for replies but I thought the main earth compliance was mandatory not something could note as non bs7671. I may be doing some bathroom wiring later in year so need to be sure all ok
If you were installing the earthing conductor as new, then yes, 16mm om a pme is the way to go, but bear in mind that bs7671 is not statutory. If the 10mm satisfies the adiabatic equation, then i would note it as a departure.
Hi
What do you think?
Thanks MATT
The 60a supply to the barn is a distribution circuit,the main earth is from the PME head to the MET at the intake....you can therefore upgrade the main earth to 16mm if required to the MET and switchfuse...the 10mm you refer to is the earth for the 60a distribution circuit,not the main earth.
why would 10mm not be big enough? the adiabatic works out less than 10mm so its meets the requirements of table 54.7 and 543.1.4 or am I missing something?
Hi Thanks for opinion but the the existing main earth comes direct from the connection at western power fuse. Each barn has its own meter and service cutout. Therefore dont think it is a disribution earth. Ther MET is at the CU.
reading wirepullers post and looking at the situation ( without seeing it.) this might be appropriate. fit a MET at the head, 16mm from head to MET, the the existing 10mm earthing conductors from this new MET to each sub-main.
Thanks, this seems a good idea. What about bonds then. Cant remember reg but sure they had to be connected to MET. If the MET is then by the service head the bonds are at the CU?
I think you are getting muddled.
543.1.1 says THE earthing conductor shall be sized according to 543.1.3 OR 543.1.4.
543.1.3 - use adiabatic equation.
543.1.4 - Where it is desired NOT to calculate the minimum csa use table 54.7 (which says the same size as the neutral up to 16mm²).
Bonding should be 10mm² for PME - Table 54.8 (or larger if DNO require).
There's also 542.3.1 which says the earthing conductor for PME shall meet the requirements of 544.1.1 for the cross sectional area of a main protective bonding conductor.
My thinking is that to be 100% compliant I could TT CU even though Ze obviusly higher but all RCD protected anyway and keep MET and bonds where they are?
You don't say how many holiday dwelling were talking about, but at the main DNO intake there should be a series of Switch Fuses or a Ryefield panel that supplies these holiday dwellings. The main earth conductor off the PME head will need to comply with PME requirements to the MET in the intake building/room. (which may require a larger conductor size than 16mm, depending on the the actual size of the DNO supply) The supplies away from this building, to the respective dwellings, are in effect distribution circuits. The individual Dwellings MET's are actually EMT's, there can only be One MET and that is always at the origin of the supply.
Personally i would have run in 3 core 16mm SWA from the intake position to the dwelling units, but you have what you have and that's a 10mm Earthing conductor. So check if it meets all the criteria, if so, it should be fine.
putting eng's post into plain english......... if it ain't broke, don't fix it. LOL. :75:
Hi
Thanks for advice. There is 6 cottages, but all have seperate western power fuses and separate meters all in one building. The appears to be no MET here. The tails and Earth travel 30m to the CU. It appears to be the same with each of the others. Although there are 6 cottages together, they are all seperate supplies and all cottages owned by different people. Therefore I am sure the MET is at the CU? I know it sounds stupid to TT a supply when it is PME but if I the main eaarth needs to be 16mm and it cant be done without digging 30m then is it not an option?
Hi,
The MET ( cable sized according to incoming supply ) should be at your intake position, ie where the meters are installed, and the 10mm cable with the 16mm tails is your supply to your CU at the Barn. At the Barn you would have installed your EMT. Just think it as being a normal install with long tails.
Regards.
Unless there is an extremely high or extremely low PFC, what on earth is wrong with a 10mm main earth on a 60A PME?!?
Required tail size is 16mm, therefore main bond will be 10mm. The main earth is sized according to the bonding conductor. Ergo sum... 10mm main earth.
I wouldn't entertain using any higher than 10mm for the main earth for any supply up to and including 100A regardless of its type (PFC permitting).
Hi
Sorry i can't envisage the set-up your describing, any chance of a photo or two of the intake building room set-up and one of the cottage supply position??
Forget any notion you may have, of degrading your earthing system, from what you have at the moment!! It not only sounds stupid, it IS stupid!! lol!!
Thought you said the supply cable to the cottage was ducted, so why would you need to excavate?? What type of conductors/cable is being used in this duct??
Unless there is an extremely high or extremely low PFC, what on earth is wrong with a 10mm main earth on a 60A PME?!? Pretty much agree with that...
Required tail size is 16mm, therefore main bond will be 10mm. The main earth is sized according to the bonding conductor. Ergo sum... 10mm main earth. ...other way round!!
I wouldn't entertain using any higher than 10mm for the main earth for any supply up to and including 100A regardless of its type (PFC permitting). I don't totally agree with that statement
I just think this is a strange distribution system, from what i can make of it so far!! lol!!
Eng on a PME system the main bond is sized according to the supply neutral. The main earth then has to be sized according to the bonding conductor (542.3.1).
PME; size the bond then the earth.
TN/TT; size the earth then the bond.
Out of interest, why don't you 'totally agree' with my last statement?
Going to bed now mate, (2.30am here) get back to you tomorrow sometime!!
it is wrong way round. the bonding conductor/s are sized according to the size of the required main earthing conductor. and while we're on it, what is the reg. no. taht says on a pme system it's got to be 16mm.
If the me is 10mm on a 60 amp main cut out I would leave it, if as you say all plots have their own fused cut outs, no multie ways anywere ie ryefield units?,but if that was the case you would have a met at the supply intake.without a pic its a bit hard good luck.
Its not the wrong way round Tel, sorry pal. See 542.3.1
don't disagree there, basically the earthing conductor must not be less than 10mm, but that's not to say it has to be >10mm.
No of course not, I don't believe I said that did I?
My point was that on a PME system you size the (minimum size of) main earth by the main bonding conductor. That's all :)
Haven't done too much in the way of PME for a good few years now, so i'll have to have a gander at the Reg's on Monday when i get back to the office to see what the so-called official version is. I can't remember sizing the main earth conductor from the bonding conductor on a PME install though.
Personally, i'd stick with the 50% rule, even with a PME installation for the main earthing conductor, especially in these day's of plastic service pipes becoming more and more prevalent in the domestic sector. To be honest, can't think of any domestic PME heads that i've seen, converted or otherwise, that had just a 10mm main earth coming off the heads N/E connection to the MET, (...may be some very early heads had a 10mm connections). It's always been 16mm, (or larger when when the head has been a substantially bigger 3 phase supply on a commercial or small industrial installation).
I'll go along with the 10mm earthing conductor in this instance though, for a known 60A supply!! I certainly wouldn't be leaving the PME connection behind in favour of a typical UK TT system that's for sure!! lol!!
Cu Change Main Earth HELP!
mcl,
D Skelton,