Am pricing for CU change for a single barn holiday cottage. Forms part of a group. All the meters are in one building at the end, approx 30m away from the CU at this barn. Seems like all ducted underground. The main fuse is 60a, and the Meter tails are 16mm so ok but the main earth (supply PME) is only 10mm2. I think it would be very difficult and costly to get 16mm upgraded main earth back to Western Power fuse.
Thought that another option is forget the PME main earth and TT locally (just other side wall with CU) to the CU?
What do you think?
Thanks MATT
Am pricing for CU change for a single barn holiday cottage. Forms part of a group. All the meters are in one building at the end, approx 30m away from the CU at this barn. Seems like all ducted underground. The main fuse is 60a, and the Meter tails are 16mm so ok but the main earth (supply PME) is only 10mm2. I think it would be very difficult and costly to get 16mm upgraded main earth back to Western Power fuse.