No i didnt do any testing before i started as it was an old wylex fuse box all the wires were short and twisted together so i thought id do it when i had finished.


My question is, where do i stand with the paperwork if the customer doesnt want to pay to get it fixed.

I did explain before i started that installing a new CU can flag up problems.


You can do an IR between lives and to earth from the busbar, no need to undo any connections.

if you explained that it can flag up problems and wrote it in your quote, i do not see the issue. You told them, there is a problem, it needs sorting.

If he won't pay it iooks like its your loss on this one. The fault needs clearing to connect to the RCD, and certify or you have just installed a white elephant in place of their wylex unit!
 
Check the obvious that your neutrals are in the right N bar!
How low are your IR readings if they are less than 0.007 MΩ then this is a good place to start from
Try and assess the cable runs to look for obvious nails, screws and so forth in the wall at odd points.
But the chances are it is just a socket outlet cable trapped or scraped.
 
Hi i went to change a CU last night and the ring main is causing the RCD to trip even with everything unplugged.

I am going back today to investigate abit more, i have just left the ring on the non RCD side for the time being.

The customer is as tight as and doesnt really want to pay for me finding a fault "as it worked before"

I am willing to spend abit of time looking for it for my own peace of mind but the house only has 1 ring so i can tell its going to be a nightmare.

Can i issue an installation certificate for the CU with low insulation resistance readings and note it in the comments?

or can i issue a EICR and recommend a rewire?

There is also no earth on the lighting but all the fittings are plastic, so i have recommended that the lights need a rewire.
TBH I am suprised you haven't been beat up over this, (message to the mods) - told you it was calmer now than a few weeks back didn't I :biggrin5:
 
recipe for disaster... starting a job when you should already be in the pub.
 
Applemac : test first .. sound advice my freind .

dont take for granted , That the ciruit is DEAD .
rewiring . two shops + 3 flats .

it was my fault for not checking the power was DEAD . 99.9% it is DEAD in my case it was 1%

my point is sound . after killing power from two flats , live cables hidden in the plaster , two of the flats have been screwing power for the shop down stair . lighting & sockets . for years . had to get a new pair of Side Cutting Pliers

After all that , the shop was feeding the some of the pub next door . aswell .

is Testing realy needed , YEAH.

Computor shop , in return the shop owner , issuded me with a new computor .
after 3 years , paying othr peoples bills , £700 electric bill he saved on . the landlord ripped up the bill .

teletix . has a vilid point .
look on the bright side. you will have learnt as lesson the hard way. you'll not make the same mistake again. Yes I have . Test , Test , Test .

sorry if mstakes , trying to work this comptor , windows 8 . word 2010
 
Possible a trapped neutral in one of the sockets , un plug every thing insulation test , it the old thing when you do a consumer upgrade "well it worked before " just explain how the RCD works with the old system working with a neutral to earth fault where as the new wont good luck in finding it
possiby a fault that a 3036 wont `see` as well....

(assuming the previous board was utilising these fuses that is)...
 
i have just left the ring on the non RCD side for the time being...The customer is as tight as and doesnt really want to pay for me finding a fault "as it worked before"...There is also no earth on the lighting but all the fittings are plastic, so i have recommended that the lights need a rewire.

Interesting as others have said that your board has a "non-RCD side".

Presumably the job is building control notifiable, is client notifying or are you on their behalf? What's going to happen about that if the sockets are not RCD protected (departs from BS7671), would you sign off on the EIC and notify with it like that?

What did you contract with the client to carry out (i.e. should fixing that ring be an extra charge)?

Don't forget the unearthed lighting warning sticker.
 
Last edited by a moderator:
Lets us have your dead test results on the ring and we might be able to shed some light also is it in twin & earth 2.5/ 1.5 or 2.5 /1.0 .

The IR readings are they in K ohms or Ohms money on a Neutral to Earth bad reading !!
 

Reply to the thread, titled "CU Change - Ring Tripping RCD Low IR" which is posted in Periodic Inspection Reporting & Certification on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
CU Change - Ring Tripping RCD Low IR
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
35

Advert

Thread statistics

Created
markthespark,
Last reply from
Ronyg,
Replies
35
Views
5,997

Advert

Back
Top