OP
WayneL
you will need to make sure you either disconnect the main earthing conductor, or test at the neutral bar with the main switch open (otherwise you'll pick up N-E at the transformer)
You don't disconnect the earthing conductor - and I should hope the main switch is open for a dead test
Jason, I don't understand why your not testing L&N connected together to earth at 250v - it's only a little croc clip fly-lead from neutral bar to bus bar - or am I missing something.