I assume Mike your meaning R1 + R2 as your talking about a shower circuit and not a ring final circuit. Yes when I do an EIC fora new installation or an addition, I do the R1 +R2 on it, as I think it is a better than the R2 only test, which I'm quite entitled to do on an EIC, and on a CU change I might just do that on a lighting circuit if there are outside lights on PIR that I don't want to start taking apart. On a PIR I have often just done an R2 only espicially on hi bay warehouse lighting. Again as the tester I deem what tests are necessary.
I really don't know where this is going, In fact after this post I do think you need some refreshing on testing. It's R1 + R2 on a shower or any other circuit,you only do r1 rn and r2 on a ring final circuit. Also you just not only do a r1 test,there is no such recognised test, I think your meanig R2 but then I'm not sure what you mean.
I'm disputing you term legitimate. Now we can bat this about as much as you wish, IMO you using the term not legitmate when referring to a 250V test is not true, it is a perfectly Legitimate test.
It is completely irrelevant if you consider it legitimate or not, that is quite rightly your opinion on it. But you can not advise others that it is not a legitmate test when in the guide we adhere to advises it is.
A lot of us time served electricians do a 250 volt LIVES/EARTH test before we even start on a CU change, it is often used as a guide, and I would be quite within my rights to do that only test and put it on the EIC if I wanted to, as it is not a departure from the regulations. I'm sure like me the majority of us do also do a 500 volt test after, if we feel it warrents it and it is not likely to damage anything. After all I'm not going to go around an entire installation disconnecting everthing, possibly taking out 30 or 40 down light lamps, disconnecting transformers, PIR or dimmers, unless I found a problem.