Hi, newbie here. Done a domestic PIR and Consumer Unit replacement is required (damaged, lighting circuit not earthed or RCDd, plus other reasons). However, another finding was that the upstairs and downstairs ring final circuits are connected (currently installed as the 2 live cables going into the circuit breaker).
Cable size is 2.5mm2.
Total floor area served is 85m2.
Circuit breaker is 32A (RCD protected).
After finding out rings were connected I did cross connected line conductor resistance test at each socket and it looks like the rings are connected at the extremity and not bridged half way round. I've deduced this as the resistance readings are almost identical to within 0.01ohm.
Customer doesn't want to fund sorting out the rings (tricky as laminate flooring and fitted furniture everywhere).
I'd appreciate views on whether it OK to proceed with CU replacement and re-energise with the rings remaining connected as they are now? Clearly it doesn't meet the suitable segregation of circuits requirement, but this appears to be the only failing. Any thoughts?
Many thanks
SW
Cable size is 2.5mm2.
Total floor area served is 85m2.
Circuit breaker is 32A (RCD protected).
After finding out rings were connected I did cross connected line conductor resistance test at each socket and it looks like the rings are connected at the extremity and not bridged half way round. I've deduced this as the resistance readings are almost identical to within 0.01ohm.
Customer doesn't want to fund sorting out the rings (tricky as laminate flooring and fitted furniture everywhere).
I'd appreciate views on whether it OK to proceed with CU replacement and re-energise with the rings remaining connected as they are now? Clearly it doesn't meet the suitable segregation of circuits requirement, but this appears to be the only failing. Any thoughts?
Many thanks