Hi, newbie here. Done a domestic PIR and Consumer Unit replacement is required (damaged, lighting circuit not earthed or RCDd, plus other reasons). However, another finding was that the upstairs and downstairs ring final circuits are connected (currently installed as the 2 live cables going into the circuit breaker).

Cable size is 2.5mm2.
Total floor area served is 85m2.
Circuit breaker is 32A (RCD protected).

After finding out rings were connected I did cross connected line conductor resistance test at each socket and it looks like the rings are connected at the extremity and not bridged half way round. I've deduced this as the resistance readings are almost identical to within 0.01ohm.

Customer doesn't want to fund sorting out the rings (tricky as laminate flooring and fitted furniture everywhere).

I'd appreciate views on whether it OK to proceed with CU replacement and re-energise with the rings remaining connected as they are now? Clearly it doesn't meet the suitable segregation of circuits requirement, but this appears to be the only failing. Any thoughts?

Many thanks
SW

Have you done r1, rn, and r2 end to end, if you have, and r1, and rn are the same, and r2 is about 1.67 times the value of either r1 or rn then you have one circuit, R1+R2 at every outlet will then show up any spurs, reverse polarity, interconnections (ring within a ring etc),and any faults like loose connections.

Cheers.......Howard
 
As it's a fairly old build you may well find a lot of it (mainly lighting) is wired as radial as well. Often done with a couple of large junction boxes (one in the loft and one under the first floor landing). Very often with dodgy cpc connections ... just the bundle of cpcs twisted together with no sleeving!
 
As it's a fairly old build you may well find a lot of it (mainly lighting) is wired as radial as well. Often done with a couple of large junction boxes (one in the loft and one under the first floor landing). Very often with dodgy cpc connections ... just the bundle of cpcs twisted together with no sleeving!
nice and easy to get a croc clip on without undoing the JB though.
 
Hello SW1970 :D

like has been said already, wouldn't worry too much, houses are laid out all sorts of ways with their socket circuits. You have more than one, plus you didn't install it, plus I agree an RCBO board would not really cost much more than a 'pain in the rear' dual RCD board.

Electrical Components and Equipment Assemblies, inc. basic, passive, marine, etc - ECD UK

I have heard these sell good stuff at good prices. Bought some myself.

I've seen houses with rings and radials all over the place, some bedrooms with three different circuits serving the sockets in that bedroom - this may make one exclaim but I think it is actually a great idea. As long as the DB is labelled / legended correctly this layout provides a higher level of 'separation' and ....resilience I suppose is the word.
 
Hi Spartykus, thanks for the input. Being new to the game I have wondered why dual RCD units are so popular compared to a unit with RCBOs. I'm aware from other posts that RCBOs can sometimes give a benefit of less nuisance tripping due to combined leakage not having so much of an effect, and are generally more convenient and perhaps more expensive, but can you guide on any reasons why a dual RCD is a pain in the rear?
 
Units with RCBOs are preferable because each circuit is independant from a leakage detection perspective. Dual RCDs, or indeed any RCD that covers more than one circuit may cause nuisance tripping due to the cumlative effect of multiple circuits (as opposed to multiple devices on a circuit).
 

Reply to CU Replacement - Upstairs and Downstairs Rings Connected in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
796
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
I fitted a Mem MR30 Pod and MCB, about ÂŁ75 for both.
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top