C

c.randall7

Hi guys got a quick question for all you pro's out there.

I'm doing a board change for an assessment and it seems a bit strange. It's a PME system with 100A main fuse, 25mm from the meter to a 63A type B DP CB then the tails drop down to 10mm T&E for about 5m to the CU. The main earth also drops down from 16mm to 10mm at this point. My first thoughts are that it's boarder line safe and not the way to do things. The max demand is less than the 63A but still not very happy with it.

My question is should i just uprate the tails and main earth (25mm, 16mm) or should i change this 63A CB as well. Bare in mind the 5m run and that it's an assessment job.

I would be greatful of any replys
 
Your meter tails and earth conductor are coorect for your 1st board however im pretty sure that 10mm t&e is not rated at 63a use amtech or the regs to check, ideally a 63a switchfuse using a BS88 fuse would be used to provide adequate discrimination along with 16mm t&e depending on installation method, the current carrying capacity drops rapidly when enclosed in trunking
 
Upgrade Tails to 25mm and earth to 16mm

as per 17th Regs PME should be NOTHING LESS for a 100amp Fuse! (p.s is it actually 100a or is that what the sticker says??) i would also change the 63a DP Isolator to a 100A DP for the sake of ÂŁ10

also ensure Main Gas and Water Bonding is Present with this sized at 10mm
 
Thanks for reply. I haven't pulled the fuse to have a look, it says soo on the wooded board it's mounted on, but i will have let the fuse 'fall out' if i'm to change the 63A switch so I'll have a look. Gas and water is 10mm but it's all terminated in the CU earth bar so i'll also fit an MET. Do you think the assesser will be happy with the 5m run? or should i fit a 100A fused DP switch?
 
the link you sent, is that not just for main switch in CU? If so the new board i'm fitting has all the rcd,s and main switch with it or can i fit that in the meter cuboard out side of the CU were the 63 is?
 
yes mate! as your Meter Tails are over 3m you need a Switch and the 100a Isolator is the Tricky!! it should be a straight swap for the 63a one! (nothing wrong with leaving the 63a one in mind) just makes its rating higher should the fuse ever be upgraded by the DNO and it can carry a higher rated current!
 
Last edited by a moderator:
The MCB is there for a reason as tails over 3M require additional overcurrent protection so you cant take it out and fit a double pole isolator, a switchfuse would be acceptable but unless you feel the max demand exceeds 63A I would leave it in.

You will need to upgrade the cpc as at 4mm, it isn't large enough to act as both cpc and main protective bonding conductor. Clipped direct a 10mm T&E will carry 64A so technically is acceptable but I wouldn't be happy leaving it and as you have to upgrade the cpc anyway you might aswell change all of it.

The 25mm tails & 16mm main earth from the meter to the MCB are fine.
 

Reply to CU/ tails chage advise in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
245
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
663
I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
508

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top