When changing a CU what cert should be given and what tests need to be done??
 
You will need to do all the useuall test on each circuit:

Continuity of protective conductors including main and supplementry bonding
Continuity of ring final circuits
Insulation resistance
Polarity
Earth loop impedence (Zs)
External impedance (Ze)
PFC


You might want to do this before you change the cu incase there is a problem with one or more of the cicuits. GN3 is a great book on the inspection & test procedure.

And you will have to notify local building control because it falls under part p.

hope this helps:)
 
Not as of yet, but as long as i issue a cert and notify building control i am ok, this is what i believe anyway??

You are right but you have to notify building control before you start the work so they can come out and see it during the work and then after and they will do an Inspection & test. This will also cost you but not sure how much. Where I live its about ÂŁ110 for jobs under ÂŁ2000. But in a near by city its about ÂŁ500, so it depends how much your lbc will charge.:confused:
 
You are right but you have to notify building control before you start the work so they can come out and see it during the work and then after and they will do an Inspection & test. This will also cost you but not sure how much. Where I live its about ÂŁ110 for jobs under ÂŁ2000. But in a near by city its about ÂŁ500, so it depends how much your lbc will charge.:confused:
quite right about notifying before work starts but i wouldnt think they would check a cu change beforehand as its all exposed

dont forget earthing and bonding before you start the work
 
Ok thanks for all the info, so if bonding is not there is it a must that it is done before the work or do i note it down on the cert and then the customer decides whether to have it done?? Also what is the best way to test the bonding or anything else that is far away from the cu, will i need an extension reel for my tester??
 
Agree Check bonding and tails etc also before a cu change i always do continuity and ir tests ! you may open up a can of worms and if you do your prepared for it !
 

Reply to CU Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
328
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

Similar threads

You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K
  • Question
You made the mistakes of a) asking the wrong question, and b) asking it at all. If you ask them, then of course they'll gold plate their...
2
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top