Isolate the installation at the main switch on the Consumer unit. Disconnect all bonding conductors to leave the final circuit CPC,s and earthing conductor connected and clamp test the Earthing conductor. If there is a current clamp test each individual CPC. If no current in earthing conductor disconnect earthing conductor and re-connect protective bonding conductors one at a time and clamp test each one .
One possible reason the water bonding is showing current is the water pipe may have a good connection to earth and the gas pipe may be isolated from earth inside the gas meter. Is the house terraced or semi-detached it has been known for cables to be connected to next door through the roof space so you are not isolated as there may be sa borrowed line from next door.
As you isolate the neutral at main switch current may be flowing through CPC and earthing conductor/bonding conductor. This may indicate a problem with the neutral connection inside the service cutout.
Still no result Try connecting everything back up and energising various circuits Ie put on all the lights, immersion heater, kettle etc and clamp test the line & neutral meter tails the currents should be equal If not clamp the earthing conductor and see if the currents add up.
Also you can try isolating the system disconnect all the cpc's from the earthing bar to isolate all cpcs from the earthing conductor and the bonding conductors and IR test between each CPC and neutral someone may have used a CPC as a neutral or connected neutral and cpc in an accessory
 
Last edited by a moderator:

Reply to current at main earth confusion in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
884

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
661
loz2754
L
  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top