neath
dont have O.S.G with me can sombody tell me the ccc for 6mm t&e buried in walls (i think i remember its 47A ) am i right
46 a is multicore
47a is single core
Table 4D2A is multicore.. ref method C.. 46A
Table 4D5 is Insulated and sheathed flat cable.. ref method C... 47A
Wouldn't T&E fall into both of these?
(single core is another table and is 47A)
No, t&e only falls in to the insulated and sheathed flat cable category, for the very simple reason that it is the insulated and sheathed flat cable that table was written for!
Reply to current carrying capacity in the UK Electrical Forum area at ElectriciansForums.net
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...
You don't normally see It in the equation. What you would normally do is apply correction factors then select a cable/conductor for Iz from It...