Current rating | on ElectriciansForums
Discuss Current rating in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Amp David
Mentor
Glossop
If the maximum power consumption of a machine is said to be 42kVA 3 phase, I worked it out to be around 58 amps. This total current must be over the 3 phases, or am i missing something.
I got it to 60.62
I may be well of the mark here, could some one please advise me where I've got wrong, If I have.
I did, 42000 / 692.8 (1.732/400)
malcolm, i have to disagree with you here.
42KW is 14kw/phase
I=14000/230=60.86. ( not allowing for power factor.)
Cheers guys,
so how come then this machine is happily running day in day out sat on a 32 a c type breaker.
love the quiet days sat at home, it makes up for the days i didn't bother listening at college:freak:
either the MCB has a good overload tolerance, or could be it's contacts are welded together. what size is the cable feeding the motor?
4mm 4 core SWA. Been installed for almost 8 years and doesn't show any signs of overheating anywhere.
Going to go in armed with my clamp meter anyway to check it out
Malc, this is what i'm thinking. I'm not the brightest spark, but even i thought that lol
I'll find the spec page for the machine and post it
Reply to Current rating in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
The total current capacity of the system in amperes is the same as the per-phase rating when referring to a balanced three-phase system. Thus, a...
Thank you, Both are heat / cool only.