All connections should be suitably enclosed (especially 12V ones) and I do not think a wago is suitably enclosed on its own.
If it were in a junction box then it would be OK.
I certainly would not crimp it, because there would be no option to easily replace the strip once it has failed.
Why is it crap? I have installed a couple of "floating" shelves in my kitchen, and rebated LED strip into them, routing the wiring through the shelf/wall. Even if I say it myself the result id nothing short of marvellous. If I knew how to do it I would upload a piccy. They can look a lot better than those old tubes if you do it properly!I wouldn't have that sort of strip lighting about me, it's crap. I'd rather go for the lights you plug into each other.
View attachment 32204There you are, snot crap is it??
Yes can't argue with any of that, you can get IP rated strip that is covered in a waterproof gel, makes a terrible stink when you solder it though! You can also fix it into the very thin mini trunking to conceal it and it helps to get it nice and straight.From a technical aspect I suppose it's just about acceptable, although I would have:
- Soldered a longer tail on and run it straight to the driver, possibly in mini trunking
- Housed the LED tape in extrusion to give a sturdier fixing and a more professional look
- Used IP rated LED strip seeing as it's in a kitchen and there's likely to be steam and bits of food flying around - there's even evidence of this in the picture
- Mounted the LED tape closer to the front of the cabinet facing downwards to light the worktop, not just to create an effect.
Apart from that it's fine.
526.5Why does a 12V connection need to be "suitably enclosed"? If it is crimped, it is easy to chop through the crimp and then re-crimp it? I can't see why a wago is not OK, you can't see it and there is no danger, it's 12v ?
526.5, 559.5.1414.4.5
12V connections tend to have higher currents than equivalent 230V and can spark badly on short circuits, for the reduction of fire risk it is best to enclose 12V connections.Why 'especially the 12V ones' Richard? They are not a shock risk, the terminations may get quite hot, but I can't see how putting in a enclosure would help, although I could be on the wrong track.
I like that, that looks good, I am not sure I could be bothered to do it for a customer though!Why is it crap? I have installed a couple of "floating" shelves in my kitchen, and rebated LED strip into them, routing the wiring through the shelf/wall. Even if I say it myself the result id nothing short of marvellous. If I knew how to do it I would upload a piccy. They can look a lot better than those old tubes if you do it properly!
View attachment 32204There you are, snot crap is it??
It's a 4 watt strip running off a 5W LED driver?? I bet I can't get a spark out of one of them if I try it tomorrow! I'll let you know..526.5
526.5, 559.5.1
12V connections tend to have higher currents than equivalent 230V and can spark badly on short circuits, for the reduction of fire risk it is best to enclose 12V connections.
Others
Fair enough on the crimps if you leave enough cable to re terminate, it is just more work later.
Reply to Cutting corners or acceptable practice? in the UK Electrical Forum area at ElectriciansForums.net